Hi Charles.

Debug output attached.  As you suspected, this is a fairly large 3-phase UPS 
running a range of live kit, so removing the supply is not an option.

Chris.

Chris Pratt
Development Infrastructure Manager
T: +44 118 929 4176 | M: +44 7979 854 307 | F: +44 118 929 4001

-----Original Message-----
From: Charles Lepple [mailto:[email protected]]
Sent: 15 July 2013 13:21
To: Pratt Chris
Cc: [email protected]
Subject: Re: [Nut-upsuser] HP R12000/3 UPS reports status as OL DISCHRG OB

On Jul 15, 2013, at 6:17 AM, Pratt Chris wrote:

> Hi.
>
> Back before Christmas Arnaud sent me a patch for the snmp-ups driver for my 
> HP R12000/3 UPS.  Unfortunately shortly after I had to take quite a lot of 
> sick leave so wasn't able to progress it, but I'm working on it again now.

Hi Chris,

Is this the patch you are referring to?

http://thread.gmane.org/gmane.comp.monitoring.nut.user/7514/focus=7546

> I'm at the point where I can start the driver with upsdrvctl and start the 
> daemon with upsd.  When I check the UPS status though it shows as OL DISCHRG 
> OB, which can't be right (it should just be OL).

Please send the debug output from starting the snmp-ups driver directly (rather 
than through upsdrvctl). That should explain why the driver is getting those 
particular status bits. Bonus points if you can show the output for both online 
as well as on-battery conditions, although I recognize that can be difficult if 
the UPS is in production use.

--
Charles Lepple
clepple@gmail




Disclaimer: This message and any attachments thereto are intended solely for 
the addressed recipient(s) and may contain confidential information.
If you are not the intended recipient, please notify the sender by reply e-mail 
and delete the e-mail (including any attachments thereto) without producing, 
distributing or retaining any copies thereof. Any review, dissemination or 
other use of, or taking of any action in reliance upon, this information by 
persons or entities other than the intended recipient(s) is prohibited.
Thank you.

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to