On 08/08/2013 10:45 PM, Tom Lane wrote:
=?ISO-8859-1?Q?Alf_H=F8gemark?= <[email protected]> writes:
I am working on improving the bcmxcp driver, to add more data reported
from the driver, and also add support for sending more commands to the ups.
The code changes are currently not part of any release, but they are in
github, and some more are on the way.
Would you be able to do some testing on your HP R3000 XR, with this
updated driver ?
I have only been able to test it on Eaton 5110 as of now. And your UPS
seems a lot more feature rich.
Cool.  Have you managed to get the 5110 to report charge/runtime data,
or is there just no hope in that direction?

                        regards, tom lane
Hi

I've added all the specified meters from the bcmxcp spec, and the driver now checks using meter map and command map received from the actual UPS, to see what the UPS supports.

Here is the output from upsc using the modified driver, for 5110, so I do not think it will possible to get more data from this model :
upsc eaton
ambient.temperature.high: 64
ambient.temperature.low: 166
battery.charge.low: 11
battery.voltage:  13.5
battery.voltage.low: 10
device.mfr: Eaton
device.model: POWERWARE UPS    500i
device.part: 103004261-5591
device.type: ups
driver.name: bcmxcp_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.shutdown_delay: 50
driver.version: 2.6.5-170-g3f72709
driver.version.internal: 0.28
input.frequency:  50.1
input.frequency.high: 55
input.frequency.low: 45
input.frequency.nominal: 50
input.quality: 0
input.transfer.boost.high: 207
input.transfer.high: 275
input.transfer.low: 178
input.transfer.trim.low: 250
input.voltage: 242
input.voltage.nominal: 230
output.current:   0.2
output.current.nominal:   1.3
output.frequency:  50.1
output.frequency.nominal: 50
output.phases: 1
output.voltage: 240
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.description: Line-Interactive UPS, Single Phase
ups.firmware: Cont:00.50 Inve:01.50
ups.load: 20
ups.mfr: Eaton
ups.model: POWERWARE UPS    500i
ups.power.nominal: 500
ups.status: OL
ups.test.result: Done and passed



You can see the changes merged into the bcmxcp branch at :
https://github.com/networkupstools/nut/tree/bcmxcp