I noted some correspondence from several years back about supporting this device with bcmxcp, and the problems therein. Since I have one of these UPS units, still going strong, and the Eaton LanSafe stuff has finally caused me enough grief to abandon it, I figured I'd take a look at this.

The issue is not that bad - the bcmxcp driver query of the topology block (2 bytes!) is returning as block 0x09 and not 0x13 . . . as per the protocol spec, "some command queries may return 0x9 even if that was not the query made" or some such verbage.

So, I made a change to bcmxcp_ser.c to handle block 0x43 a tad differently. And after this, all works - the topology *IS* correctly detected, all meters and functions show, it's golden . . . It just appears that in the firmware on this thing, that the reply to query 0x43 is a bit odd, and the authors of the initial code took far too sever an error handling path.

So, if anyone is still trying, this should get you going . . .

- Tim



--                 /* if (command <= 0x43) { */
                if (command << 0x43) {
                        if ((command - 0x30) != block_number){

ser_comm_fail("Receive error (Request command):
%x!!!\n", block_number);
                                return -1;
                        }
                }

/* Dawson - Powerware Prestige is an odd reply to topology_init . . . but works!
   Fool it into thinking it got the correct block . . . 0x13, when 0x9 is
actually returned. Maintain valid checks on all other queries. 2/2/2014 */

                if (command == 0x43) {
                        if ((command - 0x30) != 0x13){
                                ser_comm_fail("Receive error (Request comm
and): %x!!!\n", block_number);
                                return -1;
                        }
                }



================================================================================
Tim Dawson ([email protected])                    Owner/Engineer
TPC Services                                        Bellnet: (972)-221-7385
Lewisville, Texas 75067
"Gaff Tape can't fix 'Stupid', but it can muffle the sound..."