On Feb 7, 2014, at 3:44 PM, Ritter, Nicholas wrote:

> Greetings to you all,
> 
> We are attempting to use NUT to interface with a BestPower FerrUPS FE2.1KVA. 
> We are using the bestfcom driver because the driver listed our UPS as 
> supported. The driver fails, however, because "fc" commands do not exist on 
> the unit.

There is a upsdrv_init_nofc() function, but it seems to be brittle in its 
string matching.

> We are running NUT v2.7.1 on CentOS 6.5 with the bestfcom driver. We setup a 
> serial tap and see the UPS error out on the fc command issued for the model, 
> which than causes the driver to not identify the model correctly.
> 
> Does anyone have any suggestions?

See below.

> Nicholas
> 
> 
> Here are some details:
> 
> From "upsdrvctl -DDDDD start":
> 
> ------------------------------------------------------------------
> Network UPS Tools - UPS driver controller 2.7.1
>   0.000000
> If you're not a NUT core developer, chances are that you're told to enable 
> debugging
> to see why a driver isn't working for you. We're sorry for the confusion, but 
> this is
> the 'upsdrvctl' wrapper, not the driver you're interested in.
> 
> Below you'll find one or more lines starting with 'exec:' followed by an 
> absolute
> path to the driver binary and some command line option. This is what the 
> driver
> starts and you need to copy and paste that line and append the debug flags to 
> that
> line (less the 'exec:' prefix).
> 
>   0.000181    Starting UPS: ATVUPS
>   0.000194    exec:  /usr/local/ups/bin/bestfcom -a ATVUPS -u root

As the message suggests, for debugging the driver, you should bypass the 
upsdrvctl command (which really only helps when starting multiple drivers at 
once) and pass the -D flags directly to the driver:

/usr/local/ups/bin/bestfcom -a ATVUPS -u root -DDD

But I suspect that this line is not matching the spaces after the "Model:" 
string properly:

https://github.com/networkupstools/nut/blob/master/drivers/bestfcom.c#L579

Does it work if you match the exact string your model returns? If so, we can 
patch it to skip however much white space is present before the "FE".

-- 
Charles Lepple
clepple@gmail




_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser