On 16/02/14 10:03, Charles Lepple wrote:
On Feb 15, 2014, at 6:46 PM, Greg Vickers wrote:

Thanks!  I've attached the file to this email (bcmxcp_usb.output2014160926.gz), 
it ran for 12 seconds, and looks like it's looping by that time.  I'm not sure 
what to look for, does grepping for 'Yes' show the variables that the driver 
can pull off this UPS?
The boolean variables seem to be indicated by "Yes". I think the "meter map" is 
the source of the numeric variables:

    0.566550    Index   Offset  Format  NUT
    0.566617    0027    0000    51      output.frequency
    0.566680    0028    0004    51      input.frequency
    0.566743    0033    0008    51      battery.voltage
    0.566805    0041    0012    f0      battery.voltage.low
    0.566866    0043    0016    f0      battery.charge.low
    0.566928    0047    0020    f0      ups.load
    0.566989    0056    0024    f0      input.voltage
    0.567051    0065    0028    51      output.current
    0.567113    0068    0032    51      output.current.nominal
    0.567175    0078    0036    f0      output.voltage
    0.567237    0091    0040    f0      input.quality

Maybe Alf has some additional insights?

Ah, I see - I've noticed that when I browse to upsset.cgi, that there are no 
Settings reported when I select Settings and click the View button.  If I 
select the Commands function and click View, there are only four available:
- Turn off the load and return when power is back
- Turn off the load and remain off
- Start a battery test
- Description unavailable
I think Settings are what you would see from "upsrw <ups>", and Commands are listed by 
"upscmd -l <ups>". You're going to make me actually install the CGI programs, aren't you? 
Everything else I have been able to just look up in the source :-)

And correspondingly with what you say here, the same detail is returned by these commands:
$ sudo upsrw Powerware5110
$ (wow, nothing returned!)

$ sudo upscmd -l Powerware5110
Instant commands supported on UPS [Powerware5110]:
shutdown.return - Turn off the load and return when power is back
shutdown.stayoff - Turn off the load and remain off
test.battery.start - Start a battery test
test.system.start - Description unavailable

Bugger, huh. Guess I'll have to use the Windows software to set the beeper[1] to OFF. You don't have to install the cgi scripts, I'll be the guinea pig for the driver[0]!

I have a Belkin UPS which I was running on this system up to a few days ago 
when I figured out that the battery was totally cactus, and I put the Eaton 
back in until I get replacement batteries for the Belkin.  (The Belkin is two 
12v batteries, the Eaton is one.) Anyway, the driver for the Belkin actually 
has Settings reported, and I can't remember, but about 10+ different Commands.

Is the lack of Settings or Commands indicative of any problem, or is it the 
case that these just haven't been implemented on this driver?
Right, or that the protocol doesn't expose the settings or commands.

p.s. The only difference I can see from the web page any my upsc output is that 
my UPS is a 700, and the driver was developed on a 500?

The part that confuses me is why they would have the same firmware revision for 
what seem to be different sets of capabilities. Usually, the only internal 
difference between a 500 VA UPS and a 700 VA UPS is the size of the battery 
string and maybe the power electronics module.

[0] Hurmm, well, I'm happy to do any testing of code with this 700i model!
[1] Once I get replacement batteries for the 1200VA Belkin, the Powerware 5110 will be moved to hold up my weather station and wfrog laptop, so I can keep recording weather events if we lose power!