Additional question: I noticed on the HP Website that the latest version
of "CPQPOWER.MIB" (1.76, dated Sept. 19, 2013) was more recent than the
related file (./drivers/compaq-mib.c) in the NUT driver.

Is the MIB structure as implemented on the management card perhaps no
longer in line with the NUT driver ?

The latest MIB file can be downloaded from the following URL:

<https://h20565.www2.hp.com/portal/site/hpsc/template.PAGE/public/psi/swdDetails/?javax.portlet.begCacheTok=com.vignette.cachetoken&javax.portlet.endCacheTok=com.vignette.cachetoken&javax.portlet.prp_bd9b6997fbc7fc515f4cf4626f5c8d01=wsrp-navigationalState%3Didx%3D|swItem%3DMTX_d32e012fd5f14f1fb3e3859897|itemLocale%3D|mode%3D|action%3DdriverDocument&javax.portlet.tpst=bd9b6997fbc7fc515f4cf4626f5c8d01&ac.admitted=1393496865122.876444892.492883150>

TIA

Cheers. Bye.

Ph. A.


On 27/02/14 11:06, Philippe Andersson wrote:
> Hello list,
> 
> I've installed NUT on an HP blade server, and I try to get it
> communicating via SNMP with 2 HP R3000 UPSes, each fitted with a AF465A
> management card. To do this, I used the snmp-ups driver, and configured
> it for the "cpqpower" MIB. Communication with the UPSes is established.
> 
> My problem is that both UPSes constantly return the "OL OB" status
> which, in addition to being nonsensical, drives upsmon crazy (it flips
> between the two states every second).
> 
> Here is the upsc output (from one of the UPSes -- they're both similar):
> 
> -----------------------------<cut>--------------------------------
> mcbackup:/etc/ups # upsc R3000-B@localhost
> ambient.temperature: 28.0
> ambient.temperature.high: 40.00
> ambient.temperature.low: 0.00
> battery.charge: 99.00
> battery.current: 0.00
> battery.runtime: 7440.00
> battery.voltage: 13.10
> device.mfr: HP
> device.model: HP RT3000 G2 UPS
> device.serial: 3C83435450
> device.type: ups
> driver.name: snmp-ups
> driver.parameter.mibs: auto
> driver.parameter.pollfreq: 15
> driver.parameter.pollinterval: 2
> driver.parameter.port: mcups1.cal.org
> driver.parameter.snmp_version: v1
> driver.version: 2.6.5
> driver.version.data: cpqpower MIB 1.5
> driver.version.internal: 0.68
> input.current: 0.40
> input.frequency: 50.00
> input.phases: 1.00
> input.quality: 2.00
> input.voltage: 209.00
> input.voltage.nominal: 230
> outlet.1.id: 1.00
> outlet.1.status: on
> outlet.1.switchable: yes
> outlet.2.id: 2.00
> outlet.2.status: on
> outlet.2.switchable: yes
> outlet.count: 2.00
> outlet.desc: All outlets
> outlet.id: 0
> output.current: 0.20
> output.frequency: 50.00
> output.frequency.nominal: 500
> output.phases: 1.00
> output.voltage: 223.00
> output.voltage.nominal: 230
> ups.delay.shutdown: 20
> ups.delay.start: 30
> ups.firmware: 01.06.0026;01.02.0004
> ups.load: 19.00
> ups.mfr: HP
> ups.model: HP RT3000 G2 UPS
> ups.realpower: 3000.00
> ups.serial: 3C83435450
> ups.status: OL OB             <================ !!!
> ups.test.result: Unknown
> ups.timer.shutdown: 0.00
> ups.timer.start: 0.00
> ups.type: normal
> -----------------------------<cut>--------------------------------
> 
> If I use a MIB browser to inspect the .1.3.6.1.4.1.232.165.3.4.5.0 OID
> (defined in ./drivers/compaq-mib.c as "CPQPOWER_OID_POWER_STATUS"), the
> value returned by both UPSes is 3, meaning "OL" as defined in
> "cpqpower_pwr_info[]" (which is indeed the expected state for the UPS at
> present.
> 
> But if I inspect OID .1.3.6.1.4.1.232.165.3.7.3.0
> ("CPQPOWER_OID_ALARM_OB") as suggested by Arnaud, this one returns "1"
> on both UPSes (i.e. "OB", as defined in "cpqpower_alarm_ob[]") -- an
> information which is clearly inaccurate. Both UPSes are currently on
> grid power, as reported by their Web management interface.
> 
> Both UPS management cards (HP P/N AF465A) are on the latest firmware
> version (v. 1.01.013).
> 
> My system:
> OpenSUSE 13.1 64bit on HP BL460c in a C7000 enclosure
> nut-2.6.5-6.1.5.x86_64
> nut-drivers-net-2.6.5-6.1.5.x86_64
> net-snmp-5.7.2-9.1.2.x86_64
> (NUT installed from official OpenSUSE repository)
> 
> UPSes:
> UPS Name :                    HP RT3000 G2 UPS
> UPS Part Number :             AF468A
> UPS Firmware Revision :               01.02.0004
> Communication Board Firmware Revision :       01.06.0026
> Card Firmware revision :      1.01.013
> Card Part Number :            AF465A
> Card Technical Level :                05
> Card Hardware Revision :      BB
> 
> Attached is the captured trace of running the driver in debug mode.
> 
> To me, this look more and more like a bug in the Management card
> firmware. Has any one of you already experienced this? Is there a
> workaround?
> 
> TIA
> 
> Cheers. Bye.
> 
> Ph. A.
> 

-- 

*Philippe Andersson*
Unix System Administrator
IBA Particle Therapy |
Tel: +32-10-475.983
Fax: +32-10-487.707
eMail: [email protected]
<http://www.iba-worldwide.com>


Attachment: signature.asc
Description: OpenPGP digital signature

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to