On Mar 26, 2014, at 2:15 PM, Bill S wrote: > I have attached two .gz files of the driver output with the -DDDD > option. One is for when the unit is on the line AC and the the other > is when it is on battery so that there are at least two points of > reference. > > In earlier tests, I did note that when the unit was placed on battery > that the upsstats.cgi screen reported that the input voltage from 119V > to 120V and did not go to zero as I expected it would.
Hmm, I wonder if it just wasn't polling fast enough? >From the AC file: 0.263461 Report[get]: (3 bytes) => 0f 77 00 0.263469 Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 119 On battery: 0.082947 Report[get]: (3 bytes) => 0f 00 00 0.082957 Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 16, Value: 0 > I also noted that the output voltage remained at 136V. This value (136) is suspiciously a Logical Minimum that was set elsewhere in the HID Report Descriptor. AC: 0.263726 Report[get]: (3 bytes) => 12 77 00 0.263735 Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x12, Offset: 0, Size: 16, Value: 136 Note that 0x77 == 119 decimal. Battery: 0.083198 Report[get]: (3 bytes) => 12 78 00 0.083207 Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x12, Offset: 0, Size: 16, Value: 136 I will have to consult the NUT code and the HID documentation to see whether the issue is in the HID parser or the UPS HID descriptor. -- Charles Lepple clepple@gmail _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser