On Apr 5, 2014, at 7:18 AM, Mick wrote:

> $ upsrw -s "ups.delay.shutdown"="30" iDowell@localhost
> Username (suzy): admin
> Password: 
> OK

This command is sending the value to the UPS (via the usbhid-ups driver).

> $ upsc iDowell@localhost ups.delay.shutdown
> 30

And this command ends up reading the value back from the UPS.

> However, following a reboot the ups.delay.shutdown reverts to the default 
> value of 20s.  I tried running the upsrw -s command as root, but also got 20s 
> after a reboot.  This is what the access rights of the configuration files 
> look like:

The permissions are not applicable here.

The upsrw command was designed for changing variables that are typically stored 
in non-volatile memory on the UPS. Unfortunately, your UPS doesn't seem to do 
that.

Does the UPS respect the delay setting? (might be easier to see with a much 
larger delay value.) If not, there is a chance that the mappings from NUT 
variable names to HID identifiers are incorrect.

-- 
Charles Lepple