On May 27, 2014, at 9:59 PM, Daniel O'Connor wrote:

> 
> On 28 May 2014, at 10:54, Charles Lepple <[email protected]> wrote:
>> On May 26, 2014, at 8:21 PM, Daniel O'Connor wrote:
>> 
>>> However if I do either of the tests upscmd just reports 'OK' and nothing 
>>> happens.
>> 
>> Anything in syslog?
> 
> Not that I can see :(
> 
> What would log it?

The driver.

> I could try running the driver with debugging and see if that shows anything 
> of interest.

That should help. Unfortunately for non-debug operation, it appears that most 
of the usbhid-ups instcmd messages are buried at debug level 3 or 5. That 
should probably be addressed when we increase the verbosity for OL/OB events. 
(Github issue #79) The syslog() level LOG_INFO should show up in most syslog 
configurations.

>> These commands should result in a self-test similar to the periodic one (the 
>> Evolution 500 does it every two weeks), but the "OK" from upscmd doesn't 
>> actually wait for the command to be executed.
> 
> I think the new batteries will have been in for 2 weeks in a day or 2 so it 
> will be interesting to see if anything changes.


Definitely let us know. It is certainly possible that we are not sending the 
battery test command correctly, or that something is preventing it from being 
sent.

-- 
Charles Lepple