[Todd: note that it doesn't look like you are subscribed to this list. See the 
link at the bottom of this email. I'll try to CC you for now.]

On Jun 11, 2014, at 4:30 PM, Todd Bernhard wrote:

> At the company I work for, we are using many TrippLite OMNI900LCD UPSs and 
> are having difficulty setting the lower transfer threshold voltage. On our 
> other model, the Eaton MGE-3S550, this can be set using upsrw to set the 
> input.transfer.lowsetting, but on the Omni900, this option is not available. 
> In our testing, it defaults to ~95v but we want to set it to 84v.
> 
> More info:
> - OS = OpenSuse 13.1
> - Nut = nut-2.6.5-6.1.5.x86_64 (installed package from repo)
> - Driver = usbhid-ups
> - UPS = TrippLite OMNI900LCD
> 
> Are there other ways to set this value, or other drivers to try? We would 
> like to avoid writing a middleware layer to support this feature.

This driver is the only NUT driver which will work with your UPS (tripplite_usb 
is for older models with built-in USB-to-serial adapters).

I don't see any changes to drivers/tripplite-hid.c past v2.6.5 which would add 
support for that setting.

If you have access to the vendor's original software, that might be a quick 
thing to test. Some lower-end models tend not to have all of the features.

Based on the spreadsheet in an email from Tripp Lite last fall:

http://article.gmane.org/gmane.comp.monitoring.nut.user/8173

...the OMNI900LCD shares the same "protocol ID" (2010) as the SMART1000LCD, and 
the latter only seems to support "ups.delay.shutdown":

http://buildbot.networkupstools.org/~buildbot/cayman/docs/latest/ddl/Tripp_Lite/SMART1000LCD.html

If there are signs that the variable is provided by the UPS, but just missing 
from NUT, you can stop the driver, and re-run it with the following parameters 
for a minute or two. Please gzip the log before sending it.

/path/to/usbhid-ups -DD -u root -x explore -x vendorid=09ae auto > 
/tmp/OMNI900LCD.log 2>&1

Note that there are a number of unmapped vendor-specific items that might be 
the setting you are looking for:

https://github.com/networkupstools/nut/blob/master/drivers/tripplite-hid.c#L238

> Thanks much,
>  Todd Bernhard
> 
> Software Engineer
> MinuteKey, Inc
> _______________________________________________
> Nut-upsuser mailing list
> [email protected]
> http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

-- 
Charles Lepple
clepple@gmail




_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to