> Everything looks fine apart from ups.beeper.status always shows enabled > even if the status bit fom the ups has changed state.
Probably because the driver updates the beeper status only every 'pollfreq' (default 30) seconds, so it may have missed the change. > After more testing the indexes work as follows > > 0x0a = load.on / cancel.shutdown.stayoff / cancel.shutdown.return For future reference only (since the following ones are not used in the subdriver): - 0x1A -> cancel shutdown.return, - 0x2A -> cancel shutdown.stayoff, - 0x24 -> load on Are these still valid? > 0x10 and 0x18 are shutdown.stayoff and shutdown.return respectively both > with 30 sec delay > 0x20 and 0x28 = 35 sec delay > 0x30 and 0x38 = 40 sec delay > 0x40 and 0x48 = 45 sec delay > 0x50 and 0x58 = 52.5 sec delay > 0x60 and 0x68 = 60 sec delay > 0x70 and 0x78 = 2 min delay > ......... > 0xf0 and 0xf8 = 10 min delay Ah.. even easier: +0x10 (16dec) = next megatec delay Sn[Rm], n: .2 (this UPS only supports .5+) -> .9; 01 -> 10 .5 (60 * .5 = 30 seconds) -> 0x1(0|8) .6 (60 * .6 = 36 seconds) -> 0x2(0|8) ... 01 (60 * 01 = 60 seconds) -> 0x6(0|8) ... 10 (60 * 10 = 600 seconds) -> 0xF(0|8) Updated the subdriver accordingly. > The fabula driver seems to work fine apart from a problem with the LANGID ( > UPS sends 0x0009) and the driver appears to send a langid request every time > the ups is polled but apart from this everythin seems to work > If the langid_fix in ups.conf is set to 0x409 everything works fine and the > extra langid requests aren't sent That's because, when langid_fix is not set, the subdriver uses the usb_get_string_simple function (libusb/compat 0.1) that, in turn, calls the libusb_get_string_descriptor_ascii function (libusb 1.x) that first asks the device for all the supported langids and then uses the first one to get the string descriptor at the requested index. Nothing to worry about. So, to simplify the subdriver, I removed the langid thing from it. > This ups sends UPS No Ack to acknowledge everything (or not!) apart from Q1 > / F / and I (when data is actually returned) > > If you send index 0x0e or 0x0f to the UPS you receive a faulty packet / > broken pipe message (I don't know enough about usb protocols to understand > any of this. So.. *unsupported* indexes silently fail. While every *supported* index/command that fails or succeeds (obviously excluding the queries when data is returned) gets 'UPS No Ack'. Just to be sure, if you execute a beeper.toggle when the UPS is not on battery do you get 'UPS No Ack' just like when it is on battery, right? That's a bit weird as we can't discern the succeeded commands from the failed ones... at the moment the subdriver always return 0 on 'UPS No Ack': this way queries will see it as a failure while instant commands as a sucess (just like it happens with those serial devices that always reply with 'ACK' even if the command does not succeed and echo back the commands only when unknown/unsupported). This is less than ideal, but I can't find a better way to handle this situation. > One other thing I modified was a for i =0 i<10 loop I'm not sure of it's > purpose but I reduced it to i<1 because all comands other than Q1 /F and I > were repeated 10 times Since you previously said your UPS worked with the krauler subdirver, I based the fabula subdriver on it, where the loop is needed because of the crappiness of most of the supported devices that have a natural inclination to fail more often than not. As it doesn't seem to be the case here, I removed it from the fabula subdriver. Here's the updated driver: https://github.com/zykh/nut/tree/fabula-updated _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser