On Sep 11, 2014, at 9:48 PM, Stan Gammons <[email protected]> wrote:

> I have an APC USB UPS that was working on OpenBSD 5.5 with NUT 2.7.1   When I 
> installed the latest 5.6 snapshot with NUT 2.7.2 the UPS no longer sends 
> status messages when it loses line power.  I asked over on the OpenBSD ports 
> list and so far haven't had any luck getting this to work again.  I disabled 
> upd at boot as was suggested and that didn't change anything except stopping 
> the random upd detached messages.

Looking at the diffs between NUT 2.7.1 and 2.7.2 (including the OpenBSD 
patches), I don't see any changes in NUT that might cause this.

Your ProductID of 0002 is old enough not to have the broken interrupt pipe 
firmware, but that expects the OS to handle USB Interrupt In transfers 
properly. Otherwise, it will take up to 30 seconds (pollfreq) to re-fetch all 
of the variables that the UPS should provide through the Interrupt In pipe.

I would try starting the driver with "-DDD", and capture that to a log:

/usr/local/bin/usbhid-ups -DDD -a apcusb 2>&1 | tee /tmp/apcusb.log

Let it run for about two minutes, then ^C, compress the log and mail it back to 
the list.

You can also try reducing "pollfreq", although the reason for this was to 
prevent the UPS from tripping over itself by sending too much data. The 
"ups.status" bits should be polled in the fast polling cycle (2 seconds versus 
30). Hopefully the log will have some error messages to explain why that is 
apparently not happening.

-- 
Charles Lepple
clepple@gmail




_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to