On Oct 14, 2014, at 9:07 AM, Gene Heskett <[email protected]> wrote:

> On Tuesday 14 October 2014 08:19:02 Charles Lepple did opine
> And Gene did reply:
>> usbhid-ups

I apologize, I should have just mentioned the whole ups.conf:

[myups]
        driver = usbhid-ups
        port = auto

The usbhid-ups driver (as with the others based on libusb) don't actually use 
the "port =" line, but the NUT internals still need a placeholder.

There is a whole complicated set of filters that let you match on the USB 
Vendor or ProductID, but if you only have one UPS plugged in at a time, you can 
ignore them. They default to matching anything that "looks like an UPS".

> I haven't checked cabling, but AFAIK its still plugged in, but not sure if 
> its usb or serial cabling.  I'll check that once I get both eyes open 
> simultaneously and report back.
> 
> Found the cable, a D type usb, unplugged it and replugged it, and it 
> appears now to be /dev/usb/hiddev3.  dmesg, ever so helpful, and lsusb 
> equally helpful, do not tell what the /dev/usbdevice is assigned to the 
> newly discovered plugin. dmesg just reports:
> 
> [136319.530160] usb 1-10: USB disconnect, device number 2
> [136322.641716] usb 1-10: new low-speed USB device number 3 using ohci-pci

I think we take the first digit after " usb " (1) and the "device number 3", 
pad them with zeroes, and check here:

ls -l /dev/bus/usb/001/003

(Note that the NUT driver doesn't care about this path directly, but we still 
need to check permissions.)

> [136322.929480] usb 1-10: New USB device found, idVendor=050d, 
> idProduct=0751
> [136322.929486] usb 1-10: New USB device strings: Mfr=4, Product=20, 
> SerialNumber=0
> [136322.929489] usb 1-10: Product: Belkin UPS
> [136322.929491] usb 1-10: Manufacturer: Belkin 
> [136323.695058] hid-generic 0003:050D:0751.0008: hiddev0,hidraw6: USB HID 
> v1.11 Device [Belkin  Belkin UPS] on usb-0000:00:02.0-10/input0
> 
> So is this usb-0000:00:02.0-10/input0 a valid way to give nut a path to 
> it, and if so, what file do I add that too?

Nope, see previous comments about "port = auto"

> I also note that in the original bootup discovery it was hiddev0/hidraw6, 
> the same as the latest plug in report, so that also appears stable.  

Actually, if things work right, the hiddev*/hidraw* devices should disappear 
when usbhid-ups starts, leaving only the /dev/bus/usb/*/* device.

-- 
Charles Lepple
clepple@gmail




_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to