On 2014-10-20 01:05, David Gessel wrote:
I have a Smart-UPS RT 3000 XL connected via serial cable to TrueNAS 
TrueNAS-9.2.1.2-RELEASE-x64 (002022c) which runs on FreeBSD 9.2-RELEASE-p3.

When I start the NUT service, I get the message:

Oct 20 01:53:50 truenas notifier: very old or unknown APC model, support will 
be limited

Which I interpret as an indicator of less than optimal operating mode.  I 
suspect that the model identifier is not listed, though the model is likely 
pretty much a standard Smart-UPS.

This essentially means that:

- the driver has no compatiblity entries for this model
- the ups itself doesn't support command 'a' (returning its known commands/variables) - alternatively it does support 'a', but the format is somehow damaged and the driver refuses to work with it

The ups will work, but nut will treat it in "lowest common denominator" mode - no capabilities, no ability to set variables, etc. And considering the model, it's kind of surprising.

Can you start the driver in debug mode (-D option of upsdrvctl) ? There should be lots of logs produced, perhaps with some insight.

Can you connect to it directly to and issue:

Y
V
b
a
^z (ctrl-z)

and tell me what it outputs to the screen ? The commands are in order:

enter smart mode
report firmware (older method)
report firmware (newer method, might return overvoltage on old models)
report supported commands/variables
report supported capabilities