Hello again, I ran the commands again, checking to make sure the UPS was
still device 005/002, and the results is:

> root@microserver:~# ls -l /dev/bus/usb/005/002
>
> crw-rw-r-- 1 root nut 189, 513 Nov  4 12:55 /dev/bus/usb/005/002
>
>
I tried setting permissions of /dev/bus/usb/005/002 to 777 and ran the test
again to see what that would do, but there was no difference in the status
interrupt read error messages.




On 1 November 2014 23:55, Charles Lepple <[email protected]> wrote:

> On Nov 1, 2014, at 8:09 AM, jani <[email protected]> wrote:
>
> Hi Charles,
>
> Here is the output of those.  I also ran the driver a second time with
> debug level 4, just in case there were any extra hints in there.
>
>
> Here's the culprit:
>
>    5.338858 status interrupt read: error sending control message:
> Operation not permitted
>
> What does 'ls -l /dev/bus/usb/005/002' say? If the UPS has been unplugged
> since the logs were generated, replace "005/002" with the path suffix from
> this set of messages:
>
>    5.499162 Checking USB device [0001:0000] (005/002)
>    5.510156 - VendorID     : 0001
>    5.510202 - ProductID    : 0000
>    5.510209 - Manufacturer : ATCL FOR UPS
>    5.510219 - Product      : ATCL FOR UPS
>    5.510225 - Serial Number: ATCL FOR UPS
>    5.510231 - Bus          : 005
>    5.510237 Matched expected vendor='ATCL FOR UPS'.
>    5.512216 USB device [0001:0000] opened
>
> Depending on your distribution and how you installed NUT, some extra steps
> may be necessary to fix the permissions every time the UPS is plugged in.
> (NUT ships with a udev rules file.)
>
> We need to fix the logging levels - the permissions message should have
> been logged at a higher priority.
>
> _______________________________________________
> Nut-upsuser mailing list
> [email protected]
> http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
>
>
> --
> Charles Lepple
> clepple@gmail
>
>
>
>
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to