Hi Charles,
Thanks for these efforts!
On 7.11.2014 6:24, Charles Lepple wrote:
On Nov 6, 2014, at 1:44 PM, Toomas Suurmets (Priv)
<[email protected] <mailto:[email protected]>> wrote:
Hi,
Debug output of driver is attached, started with OpenUPS2 input feed
online @ 12V and going offline at 15th second of debug run.
Thanks, the voltages seem to only be off by a factor of 10:
Path: UPS.PowerSummary.Output.Voltage, Type: Feature, ReportID: 0x21,
Offset: 0, Size: 16, Value: 122.69
Path: UPS.PowerSummary.Output.Current, Type: Feature, ReportID: 0x21,
Offset: 16, Size: 16, Value: 0
Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID: 0x22,
Offset: 0, Size: 16, Value: 122.17
Not sure about the current scaling - I assumed it was also 10x too high.
I pushed a new version (0.4; ignore 0.3) which should fix the voltage
scaling.
The runtime estimate seems high, but you might need to plot that over
time to see what the scale factor should be for that. NUT usually
reports it in seconds.
Second attached file is debug output of unsuccessful UPS shutdown
captured with command:
/lib/nut/usbhid-ups -a openups -x productid=d005 -u root -DDD *-k*
2>&1 |tee openups-d005-shut.log
Not sure what to tell you - there is no shutdown command listed in the
HID descriptor. I CC'd the author of the driver - maybe the
manufacturer can provide more information?
Same thing with the configuration variables. There are a few
non-standard HID usage IDs at the end of the log, but it is not clear
how to make use of them.
--
Charles Lepple