On Nov 8, 2014, at 1:52 PM, Steve Read <[email protected]> wrote: > I have made changes but it is still the same. That is when the server gets > the lowbat/noAC signal it does shut down as expected but the slave does not. > > Perhaps it makes sense for me to list the present settings: > > On the Master: > > nut.conf > MODE=netserver > > ups.conf > [sdrups] > driver = genericups > port = /dev/ttyS1 > desc = "For Server & Backup" > upstype=9 > > upsd.conf > LISTEN 0.0.0.0 > > upsd.users > [root] > password = mypassword > upsmon master > instcmds = ALL > > upsmon.conf > MONITOR [email protected] 1 sdrups autocadba2 master
This looks good, except for the MONITOR line. Given the above settings, I think you need this: MONITOR [email protected] 1 root mypassword master > > On the Slave: > > nut.conf > MODE=netserver MODE=netclient for the slave. > upsmon.conf > MONITOR [email protected] 1 sdrups autocadba2 slave Same username/password change as above: MONITOR [email protected] 1 root mypassword slave > Master: 192.168.0.7 > Slave: 192.168.0.6 > > Dealing with the firewall I applied the following to both the master and > slave: > > sudo iptables -A INPUT -p tcp --dport 3493 -j ACCEPT > > > I have looked in the log files but have not seen anything to suggest a > problem. You should see something like this in /var/log/daemon.log: upsmon[1234]: Communications with UPS [email protected] established And something like this from netstat on the slave: $ netstat -t |grep -w nut tcp 0 0 192.168.0.6:40925 192.168.0.7:nut ESTABLISHED -- Charles Lepple clepple@gmail
_______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser