On Nov 8, 2014, at 6:12 PM, Selva Nair <[email protected]> wrote:

> Everything works rather well, except that the cgi-interface does not report 
> input/output voltages and load for the C 1500 unit. 
> upsc also reports these values only for model  1000, not for 1500. Battery 
> charge is and runtime are reported.

For the 1000, do the values match this page?

   
http://buildbot.networkupstools.org/~buildbot/cayman/docs/latest/ddl/APC/Smart-UPS_1000.html

It doesn't look like we have an entry for a C1500 yet. Would you care to submit 
the output of upsc, upsrw and upscmd -l?

> Is this a limitation of the driver, or is there way to get these data?

The driver reports values with standard USB HID names. It is possible that your 
UPS reports these using different names, or does not expose them at all over 
the standard USB HID PDC interface. Here's a quick APC protocol guide based on 
model numbers: 
http://lists.alioth.debian.org/pipermail/nut-upsdev/2014-July/006769.html

If you want to check for any hidden variables, stop the driver, and run 
"/lib/nut/usbhid-ups -a name -DDD 2>&1 | tee /tmp/APC_Smart-UPS-C1500.log" as 
root for a few minutes (it will loop endlessly; press ^C to stop). Please gzip 
the log before attaching it and sending back to the list.

-- 
Charles Lepple
clepple@gmail