On Nov 8, 2014, at 6:12 PM, Selva Nair <[email protected]> wrote: > Everything works rather well, except that the cgi-interface does not report > input/output voltages and load for the C 1500 unit. > upsc also reports these values only for model 1000, not for 1500. Battery > charge is and runtime are reported.
For the 1000, do the values match this page? http://buildbot.networkupstools.org/~buildbot/cayman/docs/latest/ddl/APC/Smart-UPS_1000.html It doesn't look like we have an entry for a C1500 yet. Would you care to submit the output of upsc, upsrw and upscmd -l? > Is this a limitation of the driver, or is there way to get these data? The driver reports values with standard USB HID names. It is possible that your UPS reports these using different names, or does not expose them at all over the standard USB HID PDC interface. Here's a quick APC protocol guide based on model numbers: http://lists.alioth.debian.org/pipermail/nut-upsdev/2014-July/006769.html If you want to check for any hidden variables, stop the driver, and run "/lib/nut/usbhid-ups -a name -DDD 2>&1 | tee /tmp/APC_Smart-UPS-C1500.log" as root for a few minutes (it will loop endlessly; press ^C to stop). Please gzip the log before attaching it and sending back to the list. -- Charles Lepple clepple@gmail