Charles,
     We did notice that there were two categories. Is there a way if we
could determine if it is colliding?

We do have a USB analyzer so I'll see if that can be used to determine if
the UPS is disconnecting due to inactivity on the bus.

Thanks!
Shade

On Tue, Nov 18, 2014 at 8:40 PM, Charles Lepple <[email protected]> wrote:

> On Nov 18, 2014, at 6:28 PM, Shade Alabsa <[email protected]> wrote:
>
> > I then noticed that in ups.conf I did not set the pollinterval, we
> normally set it to 15, so I set it to test on a RHEL 6.6 machine which
> caused this issue to happen again. On our own custom system we took the
> poll interval out and prelim testing doesn't showing the repeated
> disconnects/reconnects. I started playing more with this pollinterval and
> noticed that up to 14, exclusive, it seems to be fine.
>
> pollinterval defaults to 2, so maybe the UPS is disconnecting due to
> inactivity on the bus? (It shouldn't, but it might be a workaround for
> other systems.)
>
> The usbhid-ups driver splits the polling into two categories: "quick
> updates", to catch OL/OB/LB transitions, and "full updates" to catch
> everything else. It is possible that the higher pollinterval values are
> colliding with the pollfreq interval of 30 seconds.
>
> The UPS is requesting that the OS (or in the case of Linux, a program like
> NUT which uses libusb) poll the interrupt endpoint at least every 40 ms,
> which is fairly often, and would cause higher CPU load. The defaults in NUT
> strike a compromise.
>
> Note that the man page for the MGE SHUT driver does recommend a higher
> value of pollinterval, but that is a special case (it is essentially USB
> over a serial cable, and the baud rate is not high enough for the defaults)
> and wouldn't apply to your UPS.
>
> --
> Charles Lepple
> clepple@gmail
>
>
>
>
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to