On Jan 6, 2015, at 3:44 PM, Steve Ballantyne <[email protected]> wrote:

> Does this snippet of a failure tell you anything?  Is there something
> I can do to tell the libusb to wait a little longer for the device to
> come back?
> 
> 3118.555755     libusb_get_interrupt: Connection timed out
> 3118.557454     libusb_get_interrupt() returned 0 instead of 8 while
> sending 3a 53 ac 0d 00 00 00 00 '.S......'

These timeouts are controlled by some #defines at the beginning of the driver:

https://github.com/networkupstools/nut/blob/master/drivers/tripplite_usb.c#L231

Here is the actual loop:

https://github.com/networkupstools/nut/blob/master/drivers/tripplite_usb.c#L527

So it is trying ten times to send, and for each send attempt, it tries to 
receive ten times. These numbers are somewhat arbitrary, and are probably tuned 
more for the OMNIVS1000, but feel free to adjust them, and let me know what you 
find out.

> 3128.241548     libusb_set_report() returned 0 instead of 8
> 3128.243292     Error reading 'V' value: Device detached? (error 0:
> error sending control message: Broken pipe)
> 3128.244404     Reconnect attempt #1

This one is different - "Broken pipe" does mean an actual disconnect signal, so 
there is no getting around this plus accompanying the "data stale" message.

However, for the notifications, you could use "upssched" to only notify you if 
the UPS is disconnected for longer than the usual reconnection time.

-- 
Charles Lepple