On Jan 11, 2015, at 8:14 AM, DatGingerCat <[email protected]> wrote:

> Another interesting behaviour I found was when using the upsc command, if I 
> set the ondelay and offdelay options in the ups.conf file, about a quarter of 
> the info in the upsc output is missing (including firmware and serial number).

Hmm. To debug that, can you kill the running driver (in Debian/Ubuntu, it may 
be easiest to stop the whole nut-* service set) and manually run the driver 
with five "-D" flags (once with both ondelay and offdelay set, and once 
without), and send the stderr output from at least 60 seconds in each case? 
Probably will look something like this:

/lib/nut/usbhid-ups -a ups-name -DDDDD 2>&1 | tee 
/tmp/usbhid-ups_APC_CS650.1.log

You may want to tar and bzip2 the output (tar jcvf ...) since the log files 
grow quickly at that log level.

> Also, the timer variables in the upcs output do not change, no matter if a 
> poweroff is initiated, or a shutdown, or delayed load turning off, the timer 
> variables are always as listed in the output above.


I'll be honest, I'm not sure how this works on the Back-UPS series - on my 
Back-UPS LS500, I just use the default timers (it wasn't powering a critical 
system). I need to do some testing with another UPS, so maybe after that, I can 
swap this one in and see what happens.

-- 
Charles Lepple
clepple@gmail



_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to