On Sun, Feb 1, 2015 at 7:58 AM, Charles Lepple <[email protected]> wrote: > On Feb 1, 2015, at 7:04 AM, Melvin Call <[email protected]> wrote: > >> Thank you Charles, for the assistance and the information. Everything is >> completely functional here now. Not sure if the APC BackUPS ES550 is on the >> list of compatible devices, but it works just fine with the usbhid-ups >> driver, >> and supports several basic commands. > > You're welcome! We do have a report for the ES550, but it's for an older > version of NUT (2.2.0), and it doesn't list the supported commands: > > http://buildbot.networkupstools.org/~buildbot/cayman/docs/latest/ddl/APC/Back-UPS_ES_550.html > > If you would like, we can add the output of 'upsc' and 'upscmd -l' for your > UPS. (Feel free to mask off the serial number from the upsc output.)
Apologies for the delay, and glad to provide the output. Let me know if there is anything else I can do as well. upsc apc_es550@localhost ------------------------ battery.charge: 100 battery.charge.low: 10 battery.charge.warning: 50 battery.date: not set battery.mfr.date: 2010/12/15 battery.runtime: 1605 battery.runtime.low: 120 battery.type: PbAc battery.voltage: 13.6 battery.voltage.nominal: 12.0 device.mfr: APC device.model: Back-UPS ES 550 device.serial: xxxxxxxxxxxx device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.6.4 driver.version.data: APC HID 0.95 driver.version.internal: 0.37 input.sensitivity: medium input.transfer.high: 139 input.transfer.low: 92 input.transfer.reason: input voltage out of range input.voltage: 123.0 input.voltage.nominal: 120 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.firmware: 843.K2 .D ups.firmware.aux: K2 ups.load: 6 ups.mfr: APC ups.mfr.date: 2010/12/15 ups.model: Back-UPS ES 550 ups.productid: 0002 ups.serial: xxxxxxxxxxxx ups.status: OL ups.timer.reboot: 0 ups.timer.shutdown: -1 ups.vendorid: 051d upscmd -l apc_es550@localhost ----------------------------- beeper.disable - Disable the UPS beeper beeper.enable - Enable the UPS beeper beeper.mute - Temporarily mute the UPS beeper beeper.off - Obsolete (use beeper.disable or beeper.mute) beeper.on - Obsolete (use beeper.enable) load.off - Turn off the load immediately load.off.delay - Turn off the load with a delay (seconds) shutdown.reboot - Shut down the load briefly while rebooting the UPS shutdown.stop - Stop a shutdown in progress test.panel.start - Start testing the UPS panel test.panel.stop - Stop a UPS panel test _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser