On Feb 20, 2015, at 3:15 PM, Rob Groner <[email protected]> wrote:

> Instead, it seems that the usbhid-ups driver will search through its own list 
> of known devices with vid/pid, and won't "match" my device unless that device 
> exists as an entry in its device table.  Is that correct?

More or less, yes.

It turns out that UPS vendors all have somewhat different interpretations of 
the PDC spec.

There was an idea to create a generic fallback driver that could talk to any 
USB HID PDC device:

https://github.com/networkupstools/nut/issues/112

But at the moment, when we suggest passing the 'productid = ' parameter to 
usbhid-ups, it is because there is already a set of tables for that vendor, and 
their model is not all that different from earlier models. 

The nutdrv_qx driver might be more flexible in this regard, since we tend to 
see different VID:PID combinations for devices that all speak one of several 
easily identifiable dialects of the Megatec Q* protocols.

- Charles Lepple
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser