On Mar 30, 2015, at 10:41 AM, Jason Gould <[email protected]> wrote:

> Just started using NUT and having a problem. I’m not sure if it is even NUT 
> that is causing the issue.
> I’m running the latest FreeNAS 9.3 release.
> Network UPS Tools upsmon 2.7.2.
> The UPS is a Tripplite SU6000RT4UHVPM with the SNMPwebcard installed.
> I’m trying to use the SNMPwebcard, not USB or Serial. I’ve updated the 
> SNMPwebcard to the latest firmware version (see below).

Thanks, this is good background information.
 
> In FreeNAS I was able to create a connection to the UPS by simply adding the 
> IP address for the Port and defining the driver as “Various ups 3 (various) 
> SNMP - RFC 1628 (snmp-ups)”. After that querying it just worked via “upsc 
> tripplite”. And everything looks fine. However after a few hours I started 
> getting emails and messages in the console about communication lost (COMMBAD) 
> and shortly after it being established. This happens over and over again. I 
> thought perhaps I needed to change some of the settings in ups.conf. I tried 
> adjusting the pollfreq up to 30, using an snmp_version v2c, and a few other 
> adjustments. However the behavior persists.

There are two stages here: the snmp-ups driver polls every 'pollfreq' seconds, 
and upsmon sends a warning if an UPS is stale for longer than DEADTIME seconds 
(as set in upsmon.conf). So if you increase pollfreq, you would probably want 
to increase DEADTIME as well. (I'm not sure how FreeNAS exposes this setting.) 
The upsmon.conf documentation recommends multiplying pollfreq by three to get 
DEADTIME. You may want to go higher than that, depending on how long the 
interval is between COMMBAD and COMMOK (the messages you quoted only have 
one-minute resolution).

Unfortunately, it looks like snmp-ups goes into COMMBAD mode if even one of the 
SNMP queries fails (and it queries a lot of OIDs), so you would need to rely on 
DEADTIME to filter out any transient packet loss. You might also see if your 
firewall or switch can prioritize SNMP packets using QoS settings - I am not 
familiar with how many times NetSNMP retries, but SNMP is UDP-based.

You could also try running 'snmpwalk' by hand against the SNMPwebcard to see if 
it experiences the same packet loss. If that doesn't work, I think you have a 
case for Tripp Lite support.

-- 
Charles Lepple
clepple@gmail



_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to