On Jul 16, 2015, at 5:09 AM, dmanye <[email protected]> wrote:

> surprisingly, now both computers made the ups reboot !?!?!?!? so i've tried 
> once more and confirmed that while forcing the reboot works, the computer 
> itself does not reboot the ups when the battery is too low.

I think you figured it out: the UPS probably has another low-battery threshold, 
below which it will not start back up until it charges some more. If the UPS 
shuts down at 10%, and the power comes back briefly, there would be a period of 
time where the computer is powered, but NUT hasn't started.

Usually, this is shown as the "battery.charge.restart" variable, but  I have a 
feeling that this is one of the APC Smart-UPS models that has a lot more 
settings available via other protocols.

Here is some more background info:

http://article.gmane.org/gmane.comp.monitoring.nut.devel/6749

What does 'lsusb -d 051d: -vvv' return?

-- 
Charles Lepple
clepple@gmail




_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser