On 08/17/2015 05:42 AM, Charles Lepple wrote:
On Aug 15, 2015, at 3:15 AM, Marco Walther <[email protected]> wrote:
Hi,

I just decided to fix some scaling issues for my UPS (TRIPP-LITE 
SMART1500LCDT). Apparently that issue existed for some time (and I knew about 
it as well:-()

See http://thread.gmane.org/gmane.comp.monitoring.nut.devel/6482 for a thread.

My little patch is attached (against 2.7.3). It seems to be working better for 
me but I don't have any other TRIPP-LITE's to test that I did not break 
anything:-( So, please check it!
Hi Marco,

Thanks for the patch. I'm switching this to the nut-upsuser list to get a wider 
audience for testing.

In case others run across this problem, could you please send the output of "upsc" for your UPS, and also the 
output of "lsusb -vvv -d 09ae:"? If you want to mask out part of the serial number, it is listed in 
"ups.serial" (and "device.serial") but the more information you can leave, the better we can 
identify any patterns.

If there is firmware version information in the USB descriptors, we might want 
to limit the scaling to certain versions.

Thanks,

I'm going to start;-) Below is the info for my TRIPP-LITE SMART1500LCDT (from different times). I found a UPS.ffff00fe.UPSFirmwareVersion in the `/lib/nut/usbhid-ups -DDD -a tripplite' but nowhere else?!

I hope, this helps some people;-)
-- Marco

---------------------------------------------------------------------------------------------------
root@www:~# /bin/upsc [email protected]:3493 # With my patch;-)
Init SSL without certificate database
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 30
battery.runtime: 10800
battery.type: PbAC
battery.voltage: 27.0
battery.voltage.nominal: 24.0
device.mfr: Tripp Lite
device.model: TRIPP LITE UPS
device.serial: 2332BVLSM871901676
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 3016
driver.parameter.synchronous: no
driver.parameter.vendorid: 09ae
driver.version: 2.7.3
driver.version.data: TrippLite HID 0.81
driver.version.internal: 0.39
input.frequency: 60.1
input.transfer.high: 150.0
input.transfer.low: 92.0
input.voltage: 123.2
input.voltage.nominal: 120
output.current: 0.00
output.frequency: 60.2
output.frequency.nominal: 60
output.voltage: 124.9
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 0
ups.mfr: Tripp Lite
ups.model: TRIPP LITE UPS
ups.power: 0.0
ups.power.nominal: 1500
ups.productid: 3016
ups.serial: 2332BVLSM871901676
ups.status: OL
ups.timer.reboot: 65535
ups.timer.shutdown: 65535
ups.timer.start: 65535
ups.vendorid: 09ae
ups.watchdog.status: 0

root@www:~# lsusb -vvv -d 09ae:

Bus 002 Device 002: ID 09ae:3016 Tripp Lite
Device Descriptor:
  bLength                18
  bDescriptorType         1
  bcdUSB               1.10
  bDeviceClass            0 (Defined at Interface level)
  bDeviceSubClass         0
  bDeviceProtocol         0
  bMaxPacketSize0         8
  idVendor           0x09ae Tripp Lite
  idProduct          0x3016
  bcdDevice            0.02
  iManufacturer           3 Tripp Lite
  iProduct                1 TRIPP LITE UPS
  iSerial                 5 2332BVLSM871901676
  bNumConfigurations      1
  Configuration Descriptor:
    bLength                 9
    bDescriptorType         2
    wTotalLength           34
    bNumInterfaces          1
    bConfigurationValue     1
    iConfiguration          0
    bmAttributes         0xa0
      (Bus Powered)
      Remote Wakeup
    MaxPower              100mA
    Interface Descriptor:
      bLength                 9
      bDescriptorType         4
      bInterfaceNumber        0
      bAlternateSetting       0
      bNumEndpoints           1
      bInterfaceClass         3 Human Interface Device
      bInterfaceSubClass      0 No Subclass
      bInterfaceProtocol      0 None
      iInterface              0
        HID Device Descriptor:
          bLength                 9
          bDescriptorType        33
          bcdHID               1.11
          bCountryCode            0 Not supported
          bNumDescriptors         1
          bDescriptorType        34 Report
          wDescriptorLength     878
         Report Descriptors:
           ** UNAVAILABLE **
      Endpoint Descriptor:
        bLength                 7
        bDescriptorType         5
        bEndpointAddress     0x81  EP 1 IN
        bmAttributes            3
          Transfer Type            Interrupt
          Synch Type               None
          Usage Type               Data
        wMaxPacketSize     0x0008  1x 8 bytes
        bInterval              12
Device Status:     0x0000
  (Bus Powered)

root@www:~# /lib/nut/usbhid-ups -DDD -a tripplite
   0.000000     debug level is '3'
   0.001600     upsdrv_initups...
   0.062493     Checking device (05AC/8241) (002/003)
   0.062603     - VendorID: 05ac
   0.062633     - ProductID: 8241
   0.062656     - Manufacturer: unknown
   0.062680     - Product: unknown
   0.062703     - Serial Number: unknown
   0.062726     - Bus: 002
   0.062749     Trying to match device
   0.062794     Device does not match - skipping
   0.062831     Checking device (09AE/3016) (002/002)
   0.112678     - VendorID: 09ae
   0.112714     - ProductID: 3016
   0.112739     - Manufacturer: Tripp Lite
   0.112763     - Product: TRIPP LITE UPS
   0.112786     - Serial Number: 2332BVLSM871901676
   0.112810     - Bus: 002
   0.112833     Trying to match device
   0.112956     Device matches
0.113035 nut_usb_set_altinterface: skipped usb_set_altinterface(udev, 0) 0.117692 HID descriptor, method 1: (9 bytes) => 09 21 11 01 00 01 22 6e 03 0.117734 HID descriptor, method 2: (9 bytes) => 09 21 11 01 00 01 22 6e 03
   0.117760     HID descriptor length 878
   0.368717     Report Descriptor size = 878
0.368778 Report Descriptor: (878 bytes) => 05 84 09 04 a1 01 09 24 a1 00 85 28 09 fe 0.368827 79 01 75 08 95 01 15 00 26 ff 00 b1 03 85 29 09 ff 79 05 b1 03 85 2b 09 fd 0.368875 79 03 b1 03 09 1a a1 02 85 30 09 40 67 21 d1 f0 00 55 07 b1 83 85 31 09 30 0.368923 75 10 95 01 15 00 27 ff ff 00 00 67 21 d1 f0 00 55 01 b1 02 c0 85 11 09 5a 0.368971 75 08 95 01 15 01 25 03 65 00 55 00 b1 82 09 02 a1 02 85 32 75 01 95 07 15 0.369019 00 25 01 81 03 b1 03 09 62 95 01 b1 a2 09 62 81 a2 b1 01 81 01 09 69 b1 a2 0.369066 09 69 81 a2 95 06 b1 01 81 01 05 85 09 d0 95 01 81 a2 09 d0 b1 a2 81 01 b1 0.369115 01 95 06 09 42 09 46 09 44 09 45 09 47 09 4b 81 a2 09 42 09 46 09 44 09 45 0.369162 09 47 09 4b b1 a2 c0 85 2a 09 89 79 07 75 08 95 01 15 00 26 ff 00 b1 03 85 0.369209 62 09 8f 79 08 b1 03 85 33 09 2c b1 03 85 34 09 66 81 a2 09 66 b1 a2 85 3a 0.369256 09 29 b1 a2 85 37 09 67 b1 03 85 36 09 83 b1 03 85 38 09 8c b1 a2 85 2c 09 0.369304 8b b1 03 85 35 09 68 75 10 27 ff ff 00 00 66 01 10 55 00 81 a2 09 68 b1 a2 0.369352 c0 05 84 09 10 a1 02 09 12 a1 02 85 04 09 40 67 21 d1 f0 00 55 07 b1 02 85 0.369399 20 09 30 67 21 d1 f0 00 55 01 b1 a2 09 02 a1 02 85 23 75 01 95 02 15 00 25 0.369447 01 65 00 55 00 b1 01 95 06 05 85 09 42 09 46 09 44 09 45 09 47 09 4b b1 82 0.369495 c0 85 21 09 66 75 08 95 01 25 64 b1 a2 85 10 05 84 09 58 25 06 b1 82 c0 c0 0.369542 09 1e a1 00 85 01 09 40 26 ff 00 67 21 d1 f0 00 55 07 b1 03 85 02 09 42 66 0.369590 01 f0 55 00 b1 03 85 03 09 43 75 10 27 ff ff 00 00 66 21 d1 55 07 b1 03 c0 0.369637 09 16 a1 00 09 1a a1 02 85 18 09 30 67 21 d1 f0 00 55 01 b1 82 85 19 09 32 0.369684 66 01 f0 55 01 b1 82 c0 09 1c a1 02 85 1b 09 30 67 21 d1 f0 00 55 01 b1 82 0.369732 85 1c 09 32 66 01 f0 55 01 b1 82 85 46 09 31 67 01 00 10 00 55 01 b1 82 85 0.369779 47 09 34 66 21 d1 55 07 b1 82 85 06 09 53 67 21 d1 f0 00 55 07 b1 a2 85 09 0.369827 09 54 b1 a2 c0 09 02 a1 02 85 22 75 01 95 03 15 00 25 01 65 00 55 00 09 63 0.369875 09 6f 09 6e b1 82 95 01 b1 03 09 65 b1 82 09 6d b1 03 09 67 09 62 95 02 b1 0.369923 82 95 06 b1 03 95 01 09 72 b1 82 b1 01 c0 c0 09 18 a1 02 09 20 a1 02 85 15 0.369970 09 57 75 10 95 01 27 ff ff 00 00 66 01 10 55 00 b1 82 06 ff ff 85 16 09 56 0.370017 15 ff 26 ff 7f 35 c4 47 c4 ff 1d 00 66 01 10 b1 82 05 84 85 17 09 55 15 00 0.370064 27 ff ff 00 00 35 00 45 00 b1 82 85 61 09 56 b1 82 85 1e 09 35 75 08 26 ff 0.370157 00 65 00 b1 82 06 ff ff 85 41 09 81 66 01 10 b1 82 85 51 09 91 65 00 b1 82 0.370210 85 52 09 92 b1 82 c0 c0 06 ff ff 09 fe a1 02 75 08 95 01 15 00 26 ff 00 85 0.370258 0d 09 75 b1 03 85 0e 09 76 b1 03 85 0f 09 7c b1 82 85 6c 09 7d 75 10 27 ff 0.370305 ff 00 00 b1 03 85 a5 09 e5 b1 82 85 a6 09 e6 b1 82 85 a7 09 e7 67 21 d1 f0 0.370352 00 55 01 b1 82 85 a8 09 e8 b1 82 85 5d 09 62 75 08 95 01 26 ff 00 65 00 55 0.370400 00 b1 03 85 60 09 60 b1 03 c0 06 ff ff 09 ff a1 02 85 c2 09 d6 75 20 95 01 0.370448 27 ff ff ff 7f 17 01 00 00 80 b1 02 85 c3 09 d7 b1 02 85 e3 09 ef 75 08 95
   0.370485      07 26 ff 00 15 00 81 82 09 ef b1 82 c0 c0
   0.370901     Using subdriver: TrippLite HID 0.81
   0.377699     Report[get]: (2 bytes) => 28 01
0.377751 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28, Offset: 0, Size: 8, Value: 1
   0.381692     Report[get]: (2 bytes) => 29 05
0.381735 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 5
   0.385688     Report[get]: (2 bytes) => 2b 03
0.385731 Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x2b, Offset: 0, Size: 8, Value: 3
   0.389688     Report[get]: (2 bytes) => 30 78
0.389748 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120
   0.393691     Report[get]: (3 bytes) => 31 be 04
0.393740 Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0.001214
   0.397691     Report[get]: (2 bytes) => 11 02
0.397734 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.401690     Report[get]: (4 bytes) => 32 00 00 09
0.401735 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.401766     Report[buf]: (4 bytes) => 32 00 00 09
0.401803 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.401833     Report[buf]: (4 bytes) => 32 00 00 09
0.401870 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
   0.401900     Report[buf]: (4 bytes) => 32 00 00 09
0.401936 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
   0.401966     Report[buf]: (4 bytes) => 32 00 00 09
0.402003 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   0.402033     Report[buf]: (4 bytes) => 32 00 00 09
0.402070 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   0.402146     Report[buf]: (4 bytes) => 32 00 00 09
0.402188 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   0.402219     Report[buf]: (4 bytes) => 32 00 00 09
0.402256 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   0.402287     Report[buf]: (4 bytes) => 32 00 00 09
0.402323 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   0.402354     Report[buf]: (4 bytes) => 32 00 00 09
0.402391 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   0.402422     Report[buf]: (4 bytes) => 32 00 00 09
0.402459 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Input, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   0.402490     Report[buf]: (4 bytes) => 32 00 00 09
0.402527 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
   0.402557     Report[buf]: (4 bytes) => 32 00 00 09
0.402595 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   0.402625     Report[buf]: (4 bytes) => 32 00 00 09
0.402663 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   0.402693     Report[buf]: (4 bytes) => 32 00 00 09
0.402730 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   0.402761     Report[buf]: (4 bytes) => 32 00 00 09
0.402798 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   0.402829     Report[buf]: (4 bytes) => 32 00 00 09
0.402866 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   0.402897     Report[buf]: (4 bytes) => 32 00 00 09
0.402934 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
   0.406697     Report[get]: (2 bytes) => 2a 07
0.406741 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, Offset: 0, Size: 8, Value: 7
   0.410692     Report[get]: (2 bytes) => 62 08
0.410737 Path: UPS.PowerSummary.iOEMInformation, Type: Feature, ReportID: 0x62, Offset: 0, Size: 8, Value: 8
   0.414693     Report[get]: (2 bytes) => 33 02
0.414736 Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x33, Offset: 0, Size: 8, Value: 2
   0.418694     Report[get]: (2 bytes) => 34 64
0.418740 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   0.418769     Report[buf]: (2 bytes) => 34 64
0.418806 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   0.445699     Report[get]: (2 bytes) => 3a 0a
0.445743 Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, ReportID: 0x3a, Offset: 0, Size: 8, Value: 10
   0.457697     Report[get]: (2 bytes) => 37 64
0.457741 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x37, Offset: 0, Size: 8, Value: 100
   0.470696     Report[get]: (2 bytes) => 36 64
0.470742 Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 100
   0.483695     Report[get]: (2 bytes) => 38 1e
0.483740 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x38, Offset: 0, Size: 8, Value: 30
   0.487692     Report[get]: (2 bytes) => 2c 01
0.487735 Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x2c, Offset: 0, Size: 8, Value: 1
   0.491694     Report[get]: (3 bytes) => 35 30 2a
0.491741 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x35, Offset: 0, Size: 16, Value: 10800
   0.491771     Report[buf]: (3 bytes) => 35 30 2a
0.491809 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, Offset: 0, Size: 16, Value: 10800
   0.495691     Report[get]: (3 bytes) => 04 18 00
0.495738 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 24
   0.499696     Report[get]: (3 bytes) => 20 10 01
0.499742 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 0.000272
   0.503691     Report[get]: (2 bytes) => 23 08
0.503738 Path: UPS.BatterySystem.Battery.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x23, Offset: 2, Size: 1, Value: 0
   0.503767     Report[buf]: (2 bytes) => 23 08
0.503806 Path: UPS.BatterySystem.Battery.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x23, Offset: 3, Size: 1, Value: 1
   0.503834     Report[buf]: (2 bytes) => 23 08
0.503872 Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type: Feature, ReportID: 0x23, Offset: 4, Size: 1, Value: 0
   0.503901     Report[buf]: (2 bytes) => 23 08
0.503939 Path: UPS.BatterySystem.Battery.PresentStatus.Discharging, Type: Feature, ReportID: 0x23, Offset: 5, Size: 1, Value: 0
   0.503967     Report[buf]: (2 bytes) => 23 08
0.504006 Path: UPS.BatterySystem.Battery.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x23, Offset: 6, Size: 1, Value: 0
   0.504034     Report[buf]: (2 bytes) => 23 08
0.504072 Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x23, Offset: 7, Size: 1, Value: 0
   0.507696     Report[get]: (2 bytes) => 21 64
0.507745 Path: UPS.BatterySystem.Battery.RemainingCapacity, Type: Feature, ReportID: 0x21, Offset: 0, Size: 8, Value: 100
   0.511693     Report[get]: (2 bytes) => 10 06
0.511737 Path: UPS.BatterySystem.Battery.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 6
   0.515697     Report[get]: (2 bytes) => 01 78
0.515742 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120
   0.542700     Report[get]: (2 bytes) => 02 3c
0.542744 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60
   0.551702     Report[get]: (3 bytes) => 03 dc 05
0.551748 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 0, Size: 16, Value: 1500
   0.568704     Report[get]: (3 bytes) => 18 c7 04
0.568756 Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 0.001223
   0.581703     Report[get]: (3 bytes) => 19 5a 02
0.581751 Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 6020
   0.585695     Report[get]: (3 bytes) => 1b c4 04
0.585742 Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x1b, Offset: 0, Size: 16, Value: 0.00122
   0.589695     Report[get]: (3 bytes) => 1c 5a 02
0.589742 Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 16, Value: 6020
   0.593698     Report[get]: (3 bytes) => 46 00 00
0.593742 Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x46, Offset: 0, Size: 16, Value: 0
   0.597701     Report[get]: (3 bytes) => 47 00 00
0.597751 Path: UPS.PowerConverter.Output.ActivePower, Type: Feature, ReportID: 0x47, Offset: 0, Size: 16, Value: 0
   0.601696     Report[get]: (3 bytes) => 06 5c 00
0.601744 Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type: Feature, ReportID: 0x06, Offset: 0, Size: 16, Value: 92
   0.605697     Report[get]: (3 bytes) => 09 96 00
0.605744 Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type: Feature, ReportID: 0x09, Offset: 0, Size: 16, Value: 150
   0.609698     Report[get]: (3 bytes) => 22 20 00
0.609743 Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type: Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 0
   0.609774     Report[buf]: (3 bytes) => 22 20 00
0.609811 Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature, ReportID: 0x22, Offset: 1, Size: 1, Value: 0
   0.609840     Report[buf]: (3 bytes) => 22 20 00
0.609876 Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature, ReportID: 0x22, Offset: 2, Size: 1, Value: 0
   0.609906     Report[buf]: (3 bytes) => 22 20 00
0.609942 Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature, ReportID: 0x22, Offset: 4, Size: 1, Value: 0
   0.609971     Report[buf]: (3 bytes) => 22 20 00
0.610007 Path: UPS.PowerConverter.PresentStatus.Used, Type: Feature, ReportID: 0x22, Offset: 5, Size: 1, Value: 1
   0.610036     Report[buf]: (3 bytes) => 22 20 00
0.610073 Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type: Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0
   0.610152     Report[buf]: (3 bytes) => 22 20 00
0.610191 Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0
   0.610220     Report[buf]: (3 bytes) => 22 20 00
0.610257 Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type: Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0
   0.613694     Report[get]: (3 bytes) => 15 ff ff
0.613742 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.641704     Report[get]: (3 bytes) => 16 ff ff
0.641750 Path: UPS.OutletSystem.Outlet.TLDelayBeforeStartup, Type: Feature, ReportID: 0x16, Offset: 0, Size: 16, Value: -60
   0.649708     Report[get]: (3 bytes) => 17 ff ff
0.649761 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   0.666727     Report[get]: (3 bytes) => 61 ff ff
0.666777 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type: Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 65535
   0.670703     Report[get]: (2 bytes) => 1e 00
0.670748 Path: UPS.OutletSystem.Outlet.PercentLoad, Type: Feature, ReportID: 0x1e, Offset: 0, Size: 8, Value: 0
   0.674704     Report[get]: (2 bytes) => 41 00
0.674750 Path: UPS.OutletSystem.Outlet.ffff0081, Type: Feature, ReportID: 0x41, Offset: 0, Size: 8, Value: 0
   0.678704     Report[get]: (2 bytes) => 51 00
0.678749 Path: UPS.OutletSystem.Outlet.ffff0091, Type: Feature, ReportID: 0x51, Offset: 0, Size: 8, Value: 0
   0.682702     Report[get]: (2 bytes) => 52 00
0.682746 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.686695     Report[get]: (2 bytes) => 0d 09
0.686744 Path: UPS.ffff00fe.ffff0075, Type: Feature, ReportID: 0x0d, Offset: 0, Size: 8, Value: 9
   0.690701     Report[get]: (2 bytes) => 0e 0a
0.690752 Path: UPS.ffff00fe.ffff0076, Type: Feature, ReportID: 0x0e, Offset: 0, Size: 8, Value: 10
   0.694716     Report[get]: (2 bytes) => 0f b2
0.694763 Path: UPS.ffff00fe.UPSFirmwareVersion, Type: Feature, ReportID: 0x0f, Offset: 0, Size: 8, Value: 178
   0.699708     Report[get]: (3 bytes) => 6c 16 30
0.699754 Path: UPS.ffff00fe.CommunicationProtocolVersion, Type: Feature, ReportID: 0x6c, Offset: 0, Size: 16, Value: 12310
   0.704702     Report[get]: (3 bytes) => a5 87 00
0.704748 Path: UPS.ffff00fe.ffff00e5, Type: Feature, ReportID: 0xa5, Offset: 0, Size: 16, Value: 135
   0.709702     Report[get]: (3 bytes) => a6 02 00
0.709746 Path: UPS.ffff00fe.ffff00e6, Type: Feature, ReportID: 0xa6, Offset: 0, Size: 16, Value: 2
   0.714705     Report[get]: (3 bytes) => a7 25 00
0.714754 Path: UPS.ffff00fe.ffff00e7, Type: Feature, ReportID: 0xa7, Offset: 0, Size: 16, Value: 3.7e-05
   0.743707     Report[get]: (3 bytes) => a8 09 05
0.743754 Path: UPS.ffff00fe.ffff00e8, Type: Feature, ReportID: 0xa8, Offset: 0, Size: 16, Value: 0.001289
   0.756707     Report[get]: (2 bytes) => 5d 02
0.756751 Path: UPS.ffff00fe.ffff0062, Type: Feature, ReportID: 0x5d, Offset: 0, Size: 8, Value: 2
   0.765707     Report[get]: (2 bytes) => 60 03
0.765750 Path: UPS.ffff00fe.ffff0060, Type: Feature, ReportID: 0x60, Offset: 0, Size: 8, Value: 3
   0.770708     Report[get]: (5 bytes) => c2 0b 2f 27 69
0.770757 Path: UPS.ffff00ff.ffff00d6, Type: Feature, ReportID: 0xc2, Offset: 0, Size: 32, Value: 1.76418e+09
   0.775708     Report[get]: (5 bytes) => c3 01 0a 00 00
0.775755 Path: UPS.ffff00ff.ffff00d7, Type: Feature, ReportID: 0xc3, Offset: 0, Size: 32, Value: 2561
   0.779712     Report[get]: (8 bytes) => e3 00 00 00 00 00 00 00
0.779757 Path: UPS.ffff00ff.ffff00ef, Type: Input, ReportID: 0xe3, Offset: 0, Size: 8, Value: 0
   0.779792     Report[buf]: (8 bytes) => e3 00 00 00 00 00 00 00
0.779829 Path: UPS.ffff00ff.ffff00ef, Type: Feature, ReportID: 0xe3, Offset: 0, Size: 8, Value: 0
Network UPS Tools - Generic HID driver 0.39 (2.7.3)
USB communication driver 0.32
   0.779904     Report descriptor retrieved (Reportlen = 878)
   0.779929     Found HID device
   0.779956     Detected a UPS: Tripp Lite/TRIPP LITE UPS
   0.780063     Report[buf]: (2 bytes) => 34 64
0.780101 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   0.780172     Report[buf]: (2 bytes) => 3a 0a
0.780205 Path: UPS.PowerSummary.RemainingCapacityLimit, Type: Feature, ReportID: 0x3a, Offset: 0, Size: 8, Value: 10
   0.780266     Report[buf]: (2 bytes) => 38 1e
0.780299 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, ReportID: 0x38, Offset: 0, Size: 8, Value: 30
   0.780355     Report[buf]: (3 bytes) => 35 30 2a
0.780389 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, Offset: 0, Size: 16, Value: 10800
   0.780443     Report[buf]: (3 bytes) => 04 18 00
0.780476 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 24
   0.780529     Report[buf]: (3 bytes) => 20 10 01
0.780563 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 0.000272
   0.780621     Report[buf]: (2 bytes) => 2a 07
0.780652 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, Offset: 0, Size: 8, Value: 7
   0.790809     Report[buf]: (3 bytes) => 61 ff ff
0.790852 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type: Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 65535
   0.790924     Report[buf]: (3 bytes) => 15 ff ff
0.790958 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.791015     Report[buf]: (3 bytes) => 17 ff ff
0.791049 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   0.791113     Report[buf]: (2 bytes) => 11 02
0.791195 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.791249     Report[buf]: (3 bytes) => 03 dc 05
0.791284 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 0, Size: 16, Value: 1500
   0.791355     Report[buf]: (3 bytes) => 47 00 00
0.791387 Path: UPS.PowerConverter.Output.ActivePower, Type: Feature, ReportID: 0x47, Offset: 0, Size: 16, Value: 0
   0.791441     Report[buf]: (2 bytes) => 1e 00
0.791471 Path: UPS.OutletSystem.Outlet.PercentLoad, Type: Feature, ReportID: 0x1e, Offset: 0, Size: 8, Value: 0
   0.791540     Report[buf]: (2 bytes) => 52 00
0.791571 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.791623     Report[buf]: (4 bytes) => 32 00 00 09
0.791655 Path: UPS.PowerSummary.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0
   0.791700     Report[buf]: (4 bytes) => 32 00 00 09
0.791732 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x32, Offset: 9, Size: 1, Value: 0
   0.791781     Report[buf]: (4 bytes) => 32 00 00 09
0.791813 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   0.791860     Report[buf]: (4 bytes) => 32 00 00 09
0.791891 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   0.791939     Report[buf]: (4 bytes) => 32 00 00 09
0.791970 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   0.792019     Report[buf]: (4 bytes) => 32 00 00 09
0.792050 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   0.792097     Report[buf]: (4 bytes) => 32 00 00 09
0.792127 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   0.792175     Report[buf]: (4 bytes) => 32 00 00 09
0.792206 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   0.792254     Report[buf]: (4 bytes) => 32 00 00 09
0.792285 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x32, Offset: 23, Size: 1, Value: 0
   0.792395     Report[buf]: (3 bytes) => 22 20 00
0.792426 Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type: Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 0
   0.792472     Report[buf]: (3 bytes) => 22 20 00
0.792503 Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature, ReportID: 0x22, Offset: 1, Size: 1, Value: 0
   0.792548     Report[buf]: (3 bytes) => 22 20 00
0.792579 Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature, ReportID: 0x22, Offset: 2, Size: 1, Value: 0
   0.792636     Report[buf]: (3 bytes) => 22 20 00
0.792669 Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature, ReportID: 0x22, Offset: 4, Size: 1, Value: 0
   0.792715     Report[buf]: (3 bytes) => 22 20 00
0.792746 Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type: Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0
   0.792791     Report[buf]: (3 bytes) => 22 20 00
0.792822 Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0
   0.792867     Report[buf]: (3 bytes) => 22 20 00
0.792899 Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type: Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0
   0.792941     Report[buf]: (2 bytes) => 30 78
0.792974 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120
   0.793026     Report[buf]: (3 bytes) => 31 be 04
0.793060 Path: UPS.PowerSummary.Input.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0.001214
   0.793125     Report[buf]: (3 bytes) => 19 5a 02
0.793158 Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 6020
   0.793215     Report[buf]: (3 bytes) => 06 5c 00
0.793295 Path: UPS.PowerConverter.Output.LowVoltageTransfer, Type: Feature, ReportID: 0x06, Offset: 0, Size: 16, Value: 92
   0.793387     Report[buf]: (3 bytes) => 09 96 00
0.793421 Path: UPS.PowerConverter.Output.HighVoltageTransfer, Type: Feature, ReportID: 0x09, Offset: 0, Size: 16, Value: 150
   0.793506     Report[buf]: (2 bytes) => 01 78
0.793538 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120
   0.793592     Report[buf]: (3 bytes) => 1b c4 04
0.793637 Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x1b, Offset: 0, Size: 16, Value: 0.00122
   0.793704     Report[buf]: (3 bytes) => 46 00 00
0.793736 Path: UPS.PowerConverter.Output.Current, Type: Feature, ReportID: 0x46, Offset: 0, Size: 16, Value: 0
   0.793786     Report[buf]: (2 bytes) => 02 3c
0.793818 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60
   0.793873     Report[buf]: (3 bytes) => 1c 5a 02
0.793907 Path: UPS.PowerConverter.Output.Frequency, Type: Feature, ReportID: 0x1c, Offset: 0, Size: 16, Value: 6020
   0.794003     Report[buf]: (3 bytes) => 15 ff ff
0.794036 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.794086     Report[buf]: (3 bytes) => 61 ff ff
0.794172 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type: Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 65535
   0.794220     Report[buf]: (3 bytes) => 16 ff ff
0.794253 Path: UPS.OutletSystem.Outlet.TLDelayBeforeStartup, Type: Feature, ReportID: 0x16, Offset: 0, Size: 16, Value: -60
   0.794300     Report[buf]: (3 bytes) => 15 ff ff
0.794333 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   0.794381     Report[buf]: (3 bytes) => 17 ff ff
0.794414 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   0.794461     Report[buf]: (2 bytes) => 52 00
0.794492 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.794534     Report[buf]: (2 bytes) => 52 00
0.794565 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0
   0.794608     Report[buf]: (2 bytes) => 11 02
0.794639 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.794681     Report[buf]: (2 bytes) => 11 02
0.794712 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.794754     Report[buf]: (2 bytes) => 11 02
0.794785 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.794827     Report[buf]: (2 bytes) => 11 02
0.794858 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.794900     Report[buf]: (2 bytes) => 11 02
0.794931 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2
   0.795017     upsdrv_initinfo...
   0.795060     upsdrv_updateinfo...
   1.000739     Report[int]: (2 bytes) => 34 64
   1.000778     Got 1 HID objects...
   1.000808     Report[buf]: (2 bytes) => 34 64
1.000849 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   1.000889     Quick update...
   1.000919     Report[buf]: (3 bytes) => 61 ff ff
1.000952 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type: Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 65535
   1.000988     Report[buf]: (3 bytes) => 15 ff ff
1.001020 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   1.001056     Report[buf]: (3 bytes) => 17 ff ff
1.001087 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   1.001124     Report[buf]: (4 bytes) => 32 00 00 09
1.001155 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   1.001242     Report[buf]: (4 bytes) => 32 00 00 09
1.001275 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   1.001307     Report[buf]: (4 bytes) => 32 00 00 09
1.001337 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   1.001368     Report[buf]: (4 bytes) => 32 00 00 09
1.001398 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   1.001429     Report[buf]: (4 bytes) => 32 00 00 09
1.001458 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   1.001489     Report[buf]: (4 bytes) => 32 00 00 09
1.001519 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0 1.001685 dstate_init: sock /var/run/nut/usbhid-ups-tripplite open on fd 5
   1.001754     upsdrv_updateinfo...
   1.254734     libusb_get_interrupt: Connection timed out
   1.254774     Got 0 HID objects...
   1.254800     Quick update...
   1.254831     Report[buf]: (3 bytes) => 61 ff ff
1.254867 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type: Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 65535
   1.254904     Report[buf]: (3 bytes) => 15 ff ff
1.254936 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   1.254971     Report[buf]: (3 bytes) => 17 ff ff
1.255003 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   1.255040     Report[buf]: (4 bytes) => 32 00 00 09
1.255071 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   1.255103     Report[buf]: (4 bytes) => 32 00 00 09
1.255133 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   1.255165     Report[buf]: (4 bytes) => 32 00 00 09
1.255195 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   1.255227     Report[buf]: (4 bytes) => 32 00 00 09
1.255257 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   1.255288     Report[buf]: (4 bytes) => 32 00 00 09
1.255318 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   1.255349     Report[buf]: (4 bytes) => 32 00 00 09
1.255380 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   3.003697     upsdrv_updateinfo...
   3.255805     libusb_get_interrupt: Connection timed out
   3.255844     Got 0 HID objects...
   3.255872     Quick update...
   3.266800     Report[get]: (3 bytes) => 61 ff ff
3.266843 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type: Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 65535
   3.278794     Report[get]: (3 bytes) => 15 ff ff
3.278834 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   3.284795     Report[get]: (3 bytes) => 17 ff ff
3.284834 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   3.288790     Report[get]: (4 bytes) => 32 00 00 09
3.288828 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   3.288860     Report[buf]: (4 bytes) => 32 00 00 09
3.288891 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   3.288923     Report[buf]: (4 bytes) => 32 00 00 09
3.288953 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   3.288984     Report[buf]: (4 bytes) => 32 00 00 09
3.289014 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   3.289045     Report[buf]: (4 bytes) => 32 00 00 09
3.289135 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   3.289169     Report[buf]: (4 bytes) => 32 00 00 09
3.289199 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0
   5.005602     upsdrv_updateinfo...
   5.096879     Report[int]: (2 bytes) => 34 64
   5.096921     Got 1 HID objects...
   5.096950     Report[buf]: (2 bytes) => 34 64
5.096995 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, Offset: 0, Size: 8, Value: 100
   5.097031     Quick update...
   5.123858     Report[get]: (3 bytes) => 61 ff ff
5.123900 Path: UPS.OutletSystem.Outlet.DelayBeforeStartup, Type: Feature, ReportID: 0x61, Offset: 0, Size: 16, Value: 65535
   5.131858     Report[get]: (3 bytes) => 15 ff ff
5.131897 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535
   5.147859     Report[get]: (3 bytes) => 17 ff ff
5.147898 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535
   5.153856     Report[get]: (4 bytes) => 32 00 00 09
5.153894 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 16, Size: 1, Value: 1
   5.153927     Report[buf]: (4 bytes) => 32 00 00 09
5.153957 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 18, Size: 1, Value: 0
   5.153989     Report[buf]: (4 bytes) => 32 00 00 09
5.154019 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 19, Size: 1, Value: 1
   5.154051     Report[buf]: (4 bytes) => 32 00 00 09
5.154081 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 20, Size: 1, Value: 0
   5.154164     Report[buf]: (4 bytes) => 32 00 00 09
5.154196 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 21, Size: 1, Value: 0
   5.154228     Report[buf]: (4 bytes) => 32 00 00 09
5.154258 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 22, Size: 1, Value: 0


_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to