Roger, Ok, I simplified it somewhat. I start all of the NUT services on the command line after boot, to verify they are all starting correctly. They appear to be.
Doing this, I found the systemd service unit to somewhat reliably execute the shutdown. I only tried 5 times, but it worked each time which is a fairly significant change from previously. Still...hardly conclusive, and I'd STILL rather use the shutdown script. So I tried executing the shutdown command from the command line as well, and saw the same error that I had gotten from the systemd service unit: ----------------------------------------------------------------------------------------------- rtd@linux-5048:~> sudo /usr/local/ups/sbin/upsdrvctl -u ups start root's password: Network UPS Tools - UPS driver controller 2.7.2.6_RTD Network UPS Tools - Generic HID driver 0.39 (2.7.2.6_RTD) USB communication driver 0.32 writepid: fopen /var/run/ups/usbhid-ups-rtdups.pid: No such file or directory Using subdriver: RTD UPS HID v1.0 rtd@linux-5048:~> sudo /usr/local/ups/sbin/upsd -u ups Network UPS Tools upsd 2.7.2.6_RTD fopen /var/run/ups/upsd.pid: No such file or directory /usr/local/ups/etc/upsd.conf is world readable listening on 127.0.0.1 port 3493 Connected to UPS [rtdups]: usbhid-ups-rtdups /usr/local/ups/etc/upsd.users is world readable rtd@linux-5048:~> sudo /usr/local/ups/sbin/upsmon -u ups Network UPS Tools upsmon 2.7.2.6_RTD fopen /var/run/ups/upsmon.pid: No such file or directory UPS: rtdups@localhost (master) (power value 1) Using power down flag file /etc/killpower rtd@linux-5048:~> sudo /usr/local/ups/sbin/upsdrvctl shutdown Network UPS Tools - UPS driver controller 2.7.2.6_RTD Network UPS Tools - Generic HID driver 0.39 (2.7.2.6_RTD) USB communication driver 0.32 Can't claim USB device [2a37:5110]: No such file or directory Driver failed to start (exit status=1) ----------------------------------------------------------------------------------------------- I executed lsusb to verify the USB device is there, and it is. I tried the shutdown command again with debug enabled, but it didn't seem to reveal much more: ----------------------------------------------------------------------------------------------- rtd@linux-5048:~> sudo /usr/local/ups/sbin/upsdrvctl -DDDDD shutdown Network UPS Tools - UPS driver controller 2.7.2.6_RTD 0.000000 If you're not a NUT core developer, chances are that you're told to enable debugging to see why a driver isn't working for you. We're sorry for the confusion, but this is the 'upsdrvctl' wrapper, not the driver you're interested in. Below you'll find one or more lines starting with 'exec:' followed by an absolute path to the driver binary and some command line option. This is what the driver starts and you need to copy and paste that line and append the debug flags to that line (less the 'exec:' prefix). 0.000137 Shutdown UPS: rtdups 0.000160 exec: /usr/local/ups/bin/usbhid-ups -a rtdups -k Network UPS Tools - Generic HID driver 0.39 (2.7.2.6_RTD) USB communication driver 0.32 Can't claim USB device [2a37:5110]: No such file or directory 0.007491 Driver failed to start (exit status=1) ----------------------------------------------------------------------------------------------- I'm sure I'm doing something bone-headed, because this worked just a couple months ago without near this much trouble. Rob Groner Software Engineer Level II RTD Embedded Technologies, Inc. ISO 9001 and AS9100 Certified Ph: +1 814-234-8087 www.rtd.com -----Original Message----- From: Nut-upsuser [mailto:[email protected]] On Behalf Of Roger Price Sent: Saturday, September 05, 2015 5:13 AM To: nut-upsuser Mailing List <[email protected]> Subject: Re: [Nut-upsuser] UPS/NUT with openSUSE 13.1 On Fri, 4 Sep 2015, Rob Groner wrote: > Well, I tried the same script method with openSUSE 13.2, and it still did not > execute. > > So I tried the system method, and it worked 1 time out of 3 attempts. I > captured the last failure: > 2015-09-04T11:43:38.825317-04:00 linux-5048 upsdrvctl[1887]: Can't > claim USB device [2a37:5110]: No such file or directory > 2015-09-04T11:43:38.825970-04:00 linux-5048 upsdrvctl[1887]: Network > UPS Tools - Generic HID driver 0.39 (2.7.2.6_RTD) > 2015-09-04T11:43:38.826243-04:00 linux-5048 upsdrvctl[1887]: USB > communication driver 0.32 > 2015-09-04T11:43:38.826934-04:00 linux-5048 upsdrvctl[1887]: Driver > failed to start (exit status=1) > 2015-09-04T11:43:38.827185-04:00 linux-5048 upsdrvctl[1887]: Network > UPS Tools - UPS driver controller 2.7.2.6_RTD I'm confused here - the Bash script, and the systemd service unit, are for _shutting down_ the system on power failure, but in the trace you are having a problem _starting_ the driver. > Is it possible the USB bus is going away before that can execute? I havn't tested with openSUSE 13.2 so there may be something in it which prevents the driver from connecting to the UPS. Perhaps with a more detailed trace using the upsdrvctl -D option it may be possible to see more clearly. Roger _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser