On Sun, Jun 28, 2015 at 11:58 AM, Charles Lepple wrote:

> Another potential problem that you might see is that the driver will trigger 
> an assertion and exit when the UPS is unplugged. Theoretically, this could be 
> fixed with a launchd plist that restarts the driver, but the usual way to 
> handle this in NUT is to mark the data as stale, and wait for the UPS to 
> reappear. (Does MacPorts use a launchd plist?)

Hi Sundeep,

If you pull from the latest Git master branch of NUT (as of
2015-09-07), I fixed the assertion when the cable is unplugged. Now,
it should mark the data as stale, and you should be able to unplug and
replug the USB cable.

I did a basic sanity check with an APC Back-UPS LS500, but as
mentioned before, if you see any problems with high CPU usage, please
use the Sample Process option.

-- 
- Charles Lepple

_______________________________________________