On Sep 14, 2015, at 1:36 AM, d tbsky <[email protected]> wrote:
> 
> hi:
>    when testing nut in our environment, we found something that nut
> maybe tune for "stale/dead ups" situation. currently the "dead ups"
> are assume alive(eg: host shutdown unnecessary), unless it is in the
> "OB" state before going to stale.

Correct. "data stale" is meant to be an indication that something is wrong with 
the UPS or driver, rather than as a definitive power state. Ideally, upsmon 
sees a transition from "OL" to "OB" to "OB LB" without any intervening "data 
stale" errors.

I would recommend investigating ways around the "data stale" error, rather than 
investing time in logic that is only meant to be a last resort. The driver man 
pages mention a few cases where the NUT default timeouts might not be 
appropriate, and can be adjusted to avoid the "data stale" condition.

-- 
Charles Lepple
clepple@gmail