On Mar 6, 2016, at 1:40 AM, Mike Lee <[email protected]> wrote:
> 
> As part of the desired second configuration, I reset the UPS to report
> low battery when it had 10 minutes (600s) of estimated battery left.
> However, battery.runtime.low as reported to NUT is still the default
> of 120.

"There are 2 hard problems in computer science: cache invalidation, naming 
things, and off-by-1 errors."

-- https://twitter.com/secretGeek/status/7269997868

It seems like the NUT usbhid-ups driver is a little overzealous when it comes 
to caching UPS values associated with NUT variables: it is not refreshing 
certain variables unless they were changed through NUT.

This is due to the HU_FLAG_SEMI_STATIC flag here (so other similarly-marked 
variables would be affected as well):
https://github.com/networkupstools/nut/blob/master/drivers/apc-hid.c#L309

If you stop and start the driver, it should refresh.

I created an issue on Github so we don't forget: 
https://github.com/networkupstools/nut/issues/268

-- 