On Mar 21, 2016, at 11:23 AM, Bob Brown <[email protected]> wrote: > > I have used NUT for many years to monitor our network connected UPS > units…until recently they were all APC units. > We replaced an old APC Silcon datacenter ups with a GE LP33 unit. > It has a network card for web access and snmp support. > > How do I configure NUT to talk to the LP33 UPS unit? > Thank you.
The LP33 isn't listed in our Hardware Compatibility List, but if it uses the IETF MIB for SNMP (likely, based on one of the manuals I saw), you might just be able to change the hostname in the ups.conf entry for the old APC units. Other configuration information that might need to be changed: http://networkupstools.org/docs/man/snmp-ups.html -- Charles Lepple clepple@gmail _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser