On Apr 16, 2016, at 9:08 PM, Andy R - (NUT-List) 
<[email protected]> wrote:
> 
> It looks like you were right. I've tried building both the patch against the 
> stable 2.7.4 source and using the latest source tarball you've just created. 
> The builds both went fine and seem to run as they should. The Arch source 
> build scripts are pretty clear to manipulate at least.

If there are any URLs that you found particularly helpful for getting started 
with that, let me know. These sorts of test scenarios pop up every now and then.

> The udev rules work fine now, and  upsc/upscmd both return promising looking 
> responses. I can't actively test switching the UPS right now as it's a bit 
> late here for alarms to go off, however if there is anything more to try then 
> please let me know.
> 
> I have attached a copy of the upsc/upscmd responses to querying the UPS, and 
> the debug output of usbhid-ups from the new build in case there are any 
> anomolies that stand out.

It's going to be a little while before I can get back to this, but maybe one of 
the other NUT developers can help. One thing I did not do is try to map this to 
an equivalent Eaton model[*]. There might be additional features or fixes if 
someone knows the exact equivalent.

[*]: https://github.com/networkupstools/nut/blob/master/drivers/mge-hid.c#L89

This part looks weird, but maybe I am not used to seeing the status of a larger 
UPS: "ups.status: OL CHRG OFF" (maybe "battery.charger.status: floating" means 
float charging, rather than resting.)

If it really is off, then ups.load, ups.power and output.voltage seem 
reasonable. Otherwise, we might have an issue with scaling the values. (That 
sort of error is not common on MGE/Eaton units, but you never know.)

My personal recommendation is to do as much shutdown testing as you can before 
hooking up critical loads. It looks like "outlet.1.autoswitch.charge.low: 0" is 
off, so that should simplify testing. Also, try a battery test to see what 
messages you get in syslog. There are some procedures listed in the NUT User 
Manual for how to test shutdowns without accidentally cutting power if things 
are not configured correctly.

-- 