> On May 4, 2016, at 9:00 AM, Ken Marsh <[email protected]> wrote:
> 
>   24.578753   upsdrv_updateinfo...
>   24.831627   libusb_get_interrupt: Connection timed out
>   24.831647   Got 0 HID objects...
>   24.831661   Quick update...
>   24.881602   Path: UPS.PowerSummary.DelayBeforeStartup, Type: Feature, 
> ReportID: 0x0a, Offset: 0, Size: 32, Value: 0
>   24.931613   Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, 
> ReportID: 0x09, Offset: 0, Size: 32, Value: 0
>   24.981610   Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, 
> ReportID: 0x01, Offset: 0, Size: 1, Value: 1
>   24.981629   Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
> Feature, ReportID: 0x01, Offset: 4, Size: 1, Value: 0
>   24.981639   Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, 
> ReportID: 0x01, Offset: 2, Size: 1, Value: 1
>   24.981655   Path: 
> UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, 
> ReportID: 0x01, Offset: 1, Size: 1, Value: 0

This part is normal, if the UPS doesn't have any updates. If you trust the 
battery, you could cut power (recommended that you keep the ground and neutral 
still connected - a power strip would work) or do a battery test.

Maybe there was another driver lingering in the background before?

You can add the "pollonly" flag under [eaton] in ups.conf to see if that works 
better, but before that, I'd kill the driver and start everything normally once.

(I didn't think the driver would get that far, but for future logs, please 
redirect to a text file and attach a gzip'd version.)

-- 
Charles Lepple
clepple@gmail




_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to