On 28.05.2016 19:46, Larry Fahnoe wrote:
On Sat, May 28, 2016 at 11:05 AM, abi <[email protected]
<mailto:[email protected]>> wrote:
However I was unable to shutdown.return it. Maybe protocol is not
fully compatible?
0.145757 Initiating UPS shutdown
0.145760 upsdrv_shutdown...
0.145763 instcmd(shutdown.return, [NULL])
0.145767 powercom_shutdown_nuf: value = (null), command = 5400
0.145770 hu_find_valinfo: found 21504 (value: (null))
0.145773 Unit = 00000000, UnitExp = 0
0.145775 Exponent = 0
0.145778 PhyMax = 0, PhyMin = 0, LogMax = 65535, LogMin = 0
0.155952 Report[set]: (3 bytes) => 0f 00 54
0.155981 Set report succeeded
0.155986 instcmd: SUCCEED
When you attempted the shutdown.return, was the UPS powered or on
battery? My older Tripplite SMART2200VS won't shutdown.return unless
it is running off of batteries. When I did try shutdown.return with
the UPS powered, the tripplite_usb driver showed a similar pattern of
"libusb_get_interrupt: Connection timed out" messages.
UPS was powered. Actually, inverter of this particular UPS is broken
(but undetected by it's logic), so I was unable to test it fully. I need
UPS free of so called power race condition, however,
10.507657 refresh_report_buffer: expected 3 bytes, but got 2 instead
and
ups.timer.start: 740160
looks suspicious. As you suggest to test it on batt, I'm unsure what to
do now - get it replaced or exchange to IMPERIAL series.