On Jun 27, 2016, at 4:46 AM, Thomas Jarosch wrote:
> 
> Hello,
> 
> is there a way to query from the cmdline if the UPS data is stale?

The "data stale" state applies to the entire set of variables for an UPS, so if 
the exit code of `upsc` is zero, the data set is not stale.
> 
> "upsc" outputs a lot of information, but not if the data is stale.
> Example output from a "stale" UPS on the server:

Actually, you caught the UPS right after it was no longer stale -- otherwise, 
`upsc` would print just the "Error: Data stale" message instead of the 
variables.

> driver.name: usbhid-ups
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2

You can tune these parameters to avoid the stale condition, at the expense of 
slightly longer latency for updates. The smaller `pollinterval` (seconds 
between poll cycles) is used for items marked "HU_FLAG_QUICK_POLL" in the HID 
tables: 
https://github.com/networkupstools/nut/blob/master/drivers/apc-hid.c#L301 and 
the `pollfreq` value is used for polling the rest.

More information here: http://networkupstools.org/docs/man/usbhid-ups.html (I 
think the interrupt stuff applies to APC models with USB ID 051d:0002)

If needed, we can look at the debug output to see what is going on, but for 
whatever reason, a few "data stale" messages over the course of a day seems 
normal for many USB UPS interfaces.

-- 
Charles Lepple