[when responding, please use Reply-All - the list does not do this for you.]

> On Jul 5, 2016, at 10:01 AM, Shane Welcher <[email protected]> wrote:
> 
> I’ve tried looking for documentation on configuring NUT for Ubuntu 12.04 over 
> SNMP with a Tripplite UPS, but there isn’t a lot of SNMP configurations 
> tutorials out there from what I’ve seen. I haven’t been able to get automatic 
> shutdown to work. The driver I’ve been using is usbhid-ups which is generic 
> for Tripplite, but I’ve reviewed several other UPS driver names and some of 
> them are dedicated for SNMP. Will the usbhid-ups work for SNMP? This is the 
> UPS we use Tripp Lite SMART2200RMXL2U. I can supply more information if I 
> need to, but I’m mainly just looking for a good SNMP configuration tutorial. 
> Thank you.
> 
Ubuntu 12.04 contains NUT 2.6.3, which should be able to shutdown that UPS over 
a USB connection.

However, if you need to use SNMP, you will need the snmp-ups driver, and SNMP 
shutdown functionality was not added until 2.6.4 (in Ubuntu 14.04 and later). 

http://networkupstools.org/docs/man/snmp-ups.html

-- 
Charles Lepple
clepple@gmail




_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to