On Wed, 7 Sep 2016, Dark Penguin wrote:

First of all, please forgive me is this question has already been covered in these mailing lists; the "Search mailing list" link is dead, and I've only read the most recent monthly archives.

I often have a situation where, for one of many possible reasons, the UPS always thinks that its battery is critical. And I'm even fine with a situation when it's an emergency shutdown right from the beginning.

However, every once in a while my UPS (APC SU1000) likes to do short self-tests, and sometimes my AC power blinks for a split second. Neither of those are of any concern, but they make the UPS go into "OB LB" state for a few seconds. And just because of something insignificant like this, my whole system goes down.

A familiar problem. I use openSUSE and the UPS is an MGE/Eaton Ellipse 1500. I see wierd transient statuses such as "OL DISCHRG CHRG LB" which were bringing my box down.

Is there a way to set a timeout for "how long to wait after seeing "OB LB" before raising the FSD flag"? I want NUT to be a bit less hasty, and only shut down if it sees "OB LB" for at lest ten or even twenty seconds. I can easily spare ten more seconds of the critical state, but I want to avoid everything going down because of one second in the critical state. (That would also allow me to "train" the UPS much easier by cutting the power and knowing that I have a few seconds to turn it back on once the UPS goes to emergency beeping.)

After a lot of trial and error, I use the upssched timers as defined in the configuration file upssched.conf

 # Defective UPS shows low battery for no reason
 AT LOWBATT * EXECUTE ups-low-battery
 AT LOWBATT * START-TIMER check-low-battery-timer 5
 AT LOWBATT * START-TIMER low-battery-shutdown-timer 65

In script upssched-cmd, the event ups-low-battery logs a message suggesting a possible problem. At the timeout of check-low-battery-timer, I check the UPS status and charge. It's usually OL and 100% charged. So I send an e-mail to the sysadmin and then turn off the low-battery-shutdown-timer.

Turning off the timer is the delicate part. This is not a native NUT operation. I patched NUT 2.7.4 to add the facility of sending SIGUSR1 and SIGUSR2 to the upsd daemon. These signals create new NUT events, and allow me to add the lines

 NOTIFYMSG  SIGUSR1  "SIGUSR1 received"
 NOTIFYFLAG SIGUSR1  SYSLOG+WALL+EXEC

to upsmon.conf, and

 AT SIGUSR1 * CANCEL-TIMER low-battery-shutdown-timer

to upssched.conf.

About once a month, when the UPS gives me a false LB, I get some warnings on-screen and a summary e-mail, but the server carries on. I submitted the patches to the NUT development mailing list https://lists.alioth.debian.org/pipermail/nut-upsdev/2016-July/007202.html

Roger