fredag 9 september 2016 kl. 18:57:36 CEST skrev Jeff Bowman: > I learned earlier from Roger Price's excellent explanation that a proper > configuration includes sending a 'delayed shutdown' signal to the UPS > hardware prior to shutting down the server. >
Hi Jeff. > How is this accomplished? Does the USB driver handle this for us or must we > do something additional? It depends on the driver. Look in the manual for your driver and check if it have any extra arguments. For example the driver I was involved in "bcmxcp" has a shutdown_delay that set the time between receiving the command and actually shutting off. USBHID-UPS have a offdelay. " offdelay=num Set the timer before the UPS is turned off after the kill power command is sent (via the -k switch). The default value is 20 (in seconds). Usually this must be lower than ondelay, but the driver will not warn you upon startup if it isn’t. " You set this in the "ups.conf" file. Regards Kjell Claesson _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser