On Oct 20, 2016, at 3:22 PM, Fairfax, Charles A. wrote:
> 
> I’m having trouble with a TrippLite SU3000XLCD.  I’m using a Raspberry Pi 
> running Raspbian  (wheezy) with NUT 2.6.4. 
>  
> I can monitor my older TrippLite UPSs, mostly SU1000RT2Us, with this Pi and a 
> USB to serial adapter.

Interesting, we don't have that model number listed in our compatibility 
list[*]. Do they mostly use tripplitesu or tripplite?

[*] http://networkupstools.org/stable-hcl.html?manufacturer=Tripp%20Lite

> My first thought with the SU3000XLCD was to use the USB port instead of the 
> serial port as that’s the “modern” thing to do.  When I plugged the USB cable 
> in to the UPS it turned off, dropping the load.  The load is process control 
> instrumentation which, while not damaged, presented some challenges to 
> restart.  So now I’m leery of using the USB port.
>  
> With a long history of success monitoring UPSs via serial communication 
> that’s where I am now.  Unfortunately NUT doesn’t see the UPS.
>  
> My query is two part:
> 1)      Is there a reasonable explanation for why plugging my Pi into the 
> UPSs USB port caused it to turn off?  Is there a proper way to connect it 
> that will avoid this?  If so my problem is likely solved if the usbhid-ups 
> driver will talk to my SU3000XLCD.  If I can’t assure my employers that I 
> won’t kill  the process again USB may not be a viable option.

To be honest, I would have expected the RPi to reboot when inserting the USB 
cable.

Was the Pi plugged into a computer or a standalone USB adapter? I wonder if 
there was a difference in ground potential between the Pi and the UPS. 

The entry on the HCL for the SU3000XLCD came from NUT USB testing that Tripp 
Lite performed in their lab: 
http://article.gmane.org/gmane.comp.monitoring.nut.user/8173 . For that reason, 
I would think it would be reasonable to bother Tripp Lite about this issue, 
especially if it crops up again.

> 2)      Connecting to the serial port has not (yet) shut down the UPS.  This 
> is a good start but it would be better if communication happened.  Should I 
> be able to communicate via serial port with this SU3000XLCD with one of these 
> drivers?  Is there another driver that’s known to work with this UPS or can 
> this one be “tweaked” to work?  Can it be as simple as a baud rate mismatch?  
> I’m not having much luck querying the serial port’s settings.

Although the old "tripplite_usb" driver seems to be talking to a USB-to-serial 
chip with a very similar protocol to the "tripplite" driver, I don't think we 
ever got anywhere on trying to combine the two. Also, since the SU3000XLCD is 
listed as compatible with the usbhid-ups driver rather than tripplite_usb, I 
don't know if we can draw any conclusions from the older driver.

Do you have access to a spare SU3000XLCD? We could try patching the tripplite 
serial driver to send a protocol query, and work from there. However, I 
wouldn't want to experiment on the production system.

Another thing to note: some UPSes don't like switching between the USB and 
serial ports after they have powered up. I don't remember if we ever confirmed 
if this affects Tripp Lite hardware, but it is something to be aware of.