On Wed, 11 Jan 2017, Merk - Oliver wrote:
I've setup nas4free (latest version 11.0.0.4, which has NUT 2.7.4) in a
VM and configured it via webinterface to my APC UPS and set "shutdown
mode" to "UPS goes on battery" with a timer of 30s.
-----------------------------------------------------------------------------------------------------------
nas4free: etc# more upssched.conf
CMDSCRIPT /usr/local/bin/upssched-cmd
PIPEFN /var/run/upssched.pipe
LOCKFN /var/run/upssched.lock
AT COMMOK * EXECUTE notify
AT COMMBAD * EXECUTE notify
AT REPLBATT * EXECUTE notify
AT NOCOMM * EXECUTE notify
AT FSD * EXECUTE forced-shutdown
AT NOPARENT * EXECUTE notify
AT SHUTDOWN * EXECUTE notify
AT ONLINE * CANCEL-TIMER shutdown
AT ONLINE * EXECUTE resume
AT ONBATT * START-TIMER shutdown 30
AT ONBATT * EXECUTE shutdown-warning
AT LOWBATT * START-TIMER shutdown
AT LOWBATT * EXECUTE shutdown-warning
You have specified AT ONBATT * START-TIMER shutdown 30 which means that in
30 seconds after an OB appearing, script "/usr/local/bin/upssched-cmd
shutdown" will be called. I'm guessing that this script has forgotten to
test for "CAL" in ups.status.
You specify AT LOWBATT * START-TIMER shutdown without the timer value.
To the best of my knowledge this is undefined in NUT. Safer to specify
the timer value.
Roger