On 3/2/2017 9:57 AM, Charles Lepple wrote:
> On Dec 9, 2016, at 11:14 AM, Mike <[email protected]> wrote:
>>
>> [snip]
>>
>    0.207421   Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: 
> 0x15, Offset: 0, Size: 16, Value: -60
> 
> I haven't been able to find any information on what a "-60" would signify. 
> The value "-1" is used to cancel a timer, so maybe the internal timer is set 
> in minutes, and read back with a times-60 scale factor?
> 
> In that case, I would start by setting the "ups.delay.shutdown" and 
> "ups.delay.start" variables to multiples of 60 seconds, and try the shutdown 
> command without an argument. Using e.g. 120 and 180 will tell you whether the 
> start timer is measured from the beginning or end of the shutdown timer. 
> (Should be the latter, but no need to confuse the microcontroller any more 
> than necessary.) If that works, we can figure out why the load.off.delay 
> argument is being ignored.
> 
> You should be able to read the timer for UPS.Output.DelayBeforeShutdown via 
> the "ups.timer.shutdown" NUT variable.
> 
> Also, when testing, you may want to make sure that you have some sort of 
> dummy load on the UPS, such that "ups.load" is not zero. I am only vaguely 
> familiar with the MGE power saving features - so I am extrapolating to CPS 
> here - but I would not be surprised if the UPS ignored the shutdown delay if 
> it doesn't think there is a load attached.
> 



You were on to the correct solution with your hypothesis of the internal
timer being in minutes.

Going back to my original notes, I noticed a typo in my very first
message about this.  I had written the command I executed as:

 upscmd -u user -p password myups load.off.delay 300

when the actual command I executed was:

 upscmd -u user -p password myups load.off.delay 30



With that in mind, I tried the following command with no load:

 upscmd -u user -p password myups load.off.delay 30

and the UPS shut off immediately.  Using my new test setup, I wanted to
duplicate the results I had gotten previously.  They were duplicated.

Then I ran the command with no load:

 upscmd -u user -p password myups load.off.delay 60

and there was a 1 minute delay, then the UPS shut off.



For the rest of this message, I have a load on the UPS.

When I specify a 59 second delay on the command line, the UPS shuts off
immediately.

  59 second delay specified - immediate shutoff
  60 second delay specified - exactly one minute delay, then shutoff
  80 second delay specified - exactly one minute delay, then shutoff
 115 second delay specified - exactly one minute delay, then shutoff
 128 second delay specified - exactly two minute delay, then shutoff

So if I had to guess, I would offer that the UPS is doing an integer
divide by 60 on the number of seconds given by the command.  That is why
my request for a 30 (and 59) second delay resulted in no delay at all.


And here is the upsc command output for the UPS in question:

# upsc myups
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 1950
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 14.2
battery.voltage.nominal: 12
device.mfr: CPS
device.model: EC750G
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: CyberPower HID 0.4
driver.version.internal: 0.41
input.transfer.high: 140
input.transfer.low: 96
input.voltage: 118.0
input.voltage.nominal: 120
output.voltage: 118.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 21
ups.mfr: CPS
ups.model: EC750G
ups.productid: 0501
ups.realpower.nominal: 450
ups.status: OL
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: 0
ups.vendorid: 0764


As always, let me know if there's anything else you'd like me to try...