On 3/2/2017 9:57 AM, Charles Lepple wrote: > On Dec 9, 2016, at 11:14 AM, Mike <[email protected]> wrote: >> >> [snip] >> > 0.207421 Path: UPS.Output.DelayBeforeShutdown, Type: Feature, ReportID: > 0x15, Offset: 0, Size: 16, Value: -60 > > I haven't been able to find any information on what a "-60" would signify. > The value "-1" is used to cancel a timer, so maybe the internal timer is set > in minutes, and read back with a times-60 scale factor? > > In that case, I would start by setting the "ups.delay.shutdown" and > "ups.delay.start" variables to multiples of 60 seconds, and try the shutdown > command without an argument. Using e.g. 120 and 180 will tell you whether the > start timer is measured from the beginning or end of the shutdown timer. > (Should be the latter, but no need to confuse the microcontroller any more > than necessary.) If that works, we can figure out why the load.off.delay > argument is being ignored. > > You should be able to read the timer for UPS.Output.DelayBeforeShutdown via > the "ups.timer.shutdown" NUT variable. > > Also, when testing, you may want to make sure that you have some sort of > dummy load on the UPS, such that "ups.load" is not zero. I am only vaguely > familiar with the MGE power saving features - so I am extrapolating to CPS > here - but I would not be surprised if the UPS ignored the shutdown delay if > it doesn't think there is a load attached. >
You were on to the correct solution with your hypothesis of the internal timer being in minutes. Going back to my original notes, I noticed a typo in my very first message about this. I had written the command I executed as: upscmd -u user -p password myups load.off.delay 300 when the actual command I executed was: upscmd -u user -p password myups load.off.delay 30 With that in mind, I tried the following command with no load: upscmd -u user -p password myups load.off.delay 30 and the UPS shut off immediately. Using my new test setup, I wanted to duplicate the results I had gotten previously. They were duplicated. Then I ran the command with no load: upscmd -u user -p password myups load.off.delay 60 and there was a 1 minute delay, then the UPS shut off. For the rest of this message, I have a load on the UPS. When I specify a 59 second delay on the command line, the UPS shuts off immediately. 59 second delay specified - immediate shutoff 60 second delay specified - exactly one minute delay, then shutoff 80 second delay specified - exactly one minute delay, then shutoff 115 second delay specified - exactly one minute delay, then shutoff 128 second delay specified - exactly two minute delay, then shutoff So if I had to guess, I would offer that the UPS is doing an integer divide by 60 on the number of seconds given by the command. That is why my request for a 30 (and 59) second delay resulted in no delay at all. And here is the upsc command output for the UPS in question: # upsc myups battery.charge: 100 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 1950 battery.runtime.low: 300 battery.type: PbAcid battery.voltage: 14.2 battery.voltage.nominal: 12 device.mfr: CPS device.model: EC750G device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.parameter.synchronous: no driver.version: 2.7.4 driver.version.data: CyberPower HID 0.4 driver.version.internal: 0.41 input.transfer.high: 140 input.transfer.low: 96 input.voltage: 118.0 input.voltage.nominal: 120 output.voltage: 118.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 21 ups.mfr: CPS ups.model: EC750G ups.productid: 0501 ups.realpower.nominal: 450 ups.status: OL ups.test.result: No test initiated ups.timer.shutdown: -60 ups.timer.start: 0 ups.vendorid: 0764 As always, let me know if there's anything else you'd like me to try... Thanks for the assist! _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser