2017-04-04 14:18 GMT+02:00 Jon Bendtsen <[email protected]>:

> On 04/04/17 14.10, Roger Price wrote:
>
>> On Tue, 4 Apr 2017, Arnaud Quette wrote:
>>
>>
> [cuuuuut]
>
> Hi Arnaud, It seems to me that, looking out into the future, there are
>> three
>> things upsmon needs:
>>
>> 1. A fall-through <notify type> of "UNKNOWN" so that all status changes,
>> no
>> matter how wierd, can be caught.  Such a catch-all <notify type> would
>> also have
>> caught the "ALARM" from the old battery.
>>
>> 2. A UPS specific option in the NOTIFYFLAG and NOTIFYMSG declarations as
>> already
>> provided by the AT declaration in upssched.conf.  This would make it
>> possible to
>> have messages and action specific to a UPS, in a multi-UPS configuration.
>>
>> I would like to be able to specify
>>
>>    NOTIFYMSG myups@localhost      ONBATT "%s: local UPS on battery"
>>    NOTIFYMSG bigups@server        ONBATT "%s: Server room alert: UPS on
>> battery"
>>
>>    NOTIFYFLAG myups@localhost     ONBATT SYSLOG+EXEC+WALL
>>    NOTIFYFLAG heartbeat@localhost ONBATT SYSLOG+EXEC
>>
>> 3. A <notify type> "ALARM" as you propose.
>>
>
> good ideas
>

there is a Github issue: https://github.com/networkupstools/nut/issues/415
+ a branch with the implementation:
https://github.com/networkupstools/nut/tree/upsmon_alarm

For now:
- upsmon can react on the ALARM notify type, as with other events, and
WALL+SYSLOG+EXEC...
- I've also fixed the CGI to expose the ALARM flag, which was not done.

A possible improvement would be to send the content of ups.alarm, but that
requires more thinking and time.
And the current implementation already points at this data.

@Jon: would you be able to test this branch and ack? (including the "covers
(or not) my needs...)

thanks and cheers,
Arno
-- 
Eaton Data Center Automation Solutions - Opensource Leader -
http://42ity.org
NUT (Network UPS Tools) Project Leader - http://www.networkupstools.org
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.fr
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to