On Jan 22, 2018, at 3:00 PM, Ken Olum <[email protected]> wrote:
> 
> I tested the effect of setting UPS.OutletSystem.Outlet.DelayBeforeShutdown
> using Tripp Lite's software, which appears to be as follows:
> 
Theoretically, this should be the same as running the command "upscmd 
bcpers@localhost -u <upsd.user> load.off.delay <delay>".

> So if you could fix nut to use UPS.OutletSystem.Outlet.DelayBeforeShutdown
> in my case, or tell me how do it, I would appreciate that.

I still haven't had a good chunk of time to walk through the shutdown code (the 
part that handles "usbhid-ups ... -k"), but in the mean time, would you be 
interested in setting things up to rebuild the driver? (The next week is 
looking pretty ridiculous for me, so I don't anticipate being able to dust off 
my .deb build tree soon.)

My thought is that you can rebuild NUT with the same configuration options as 
the .debs, and the usbhid-ups driver should just drop in. The instructions are 
almost the same for Ubuntu as for Debian:

http://lists.alioth.debian.org/pipermail/nut-upsdev/2017-October/007341.html and

http://lists.alioth.debian.org/pipermail/nut-upsdev/2017-October/007343.html 
(omit the "git checkout" line; although we have a new-and-improved libusb 
branch, I think it's an unnecessary delta for your situation.)