One more thing. Geographical redundancy is a good thing. -brian

On 7/27/07, Brian Gupta <[EMAIL PROTECTED]> wrote:
>
> You want enough battery time to start the generators, and fix the
> generators and pumps that may possibly fail. (And you definately want to
> make sure you have redundant fuel pumps for each generator.)
>
> Also quarterly testing is a must.
>
> --brian
>
> On 7/27/07, Bill Sommerfeld <[EMAIL PROTECTED]> wrote:
> >
> > On Tue, 2007-07-24 at 22:20 -0700, Hugh McIntyre wrote:
> >
> > > http://www.prnewswire.com/cgi-bin/stories.pl?ACCT=104&STORY=/www/story/07-24-2007/0004631109&EDATE=
> >
> > >
> > > In answer to the questions about backup power, obviously they have UPS
> > > and generators (as the press release says...).
> >
> > There is more detail available here:
> >
> > http://www.365main.com/status_update.html
> >
> > Looks like they had  8 primary and 2 secondary generators - N+2
> > redundancy.
> >
> > They lost 5 -- 4 failed to start, and another was overloaded into
> > failure due to the first 4 failures.
> >
> > At first, three primary and one secondary generator failed to come up.
> >
> > It appears there was sufficient capacity in the remaining secondary
> > generator to handle the load of two of the primaries, but not three, so
> > the running secondary generator *also* fell over.
> >
> > As a result, three of their eight rooms lost power for about 45 minutes;
> > a fourth room lost power for half a second due to some sort of PDU
> > glitch.
> >
> >                                         - Bill
> >
> >
> >
> >
> >