>>> Latest update from AT&T:
>>>
>>>
>>>
>>> AT&T Corporate Real Estate teams are now gathering on site after
>pausing
>>> work last night due a fire that reignited on site around midnight.
>The Fire
>>> Marshall has joined the AT&T team to provide official approval to
>proceed.
>>> Last night, the teams were able to accomplish testing the busbar,
>placing
>>> the temporary generators, completing power cabling, and opening all
>the
>>> breakers on the individual floors. It is estimated that this round
>of power
>>> related work is about 75% complete. The target is for energizing is
>1200
>>> CST. A partial analysis by the AT&T Structural Engineer initial
>found no
>>> concrete or steel damage that caused major concern. Once team
>re-engage
>>> this morning, they will complete their full analysis and ensure it
>is safe
>>> for restoration crews to proceed. AT&T Mechanical Engineers have
>confirmed
>>> there is roughly 3 feet of water in the basement with potential
>damage to
>>> mechanical equipment in that area. It is also suspected that
>commercial
>>> power may not be available for some time and as a result power will
>come
>>> from AT&T and Tennessee Emergency Management Agency generators.
>Additional
>>> technician support will be made available rotating over a 24 hour
>period.
>>>
>>> Core CBB teams continue to work on the secondary plan to reroute
>around
>>> the Nashville 2nd Ave location. They had some success this morning
>at 05:05
>>> CT when core connectivity was established for the Winchester, KY
>office.
>>> Partial 911 connectivity has been restored in that specific area.
>Work will
>>> continue on the CBB reroute plans in several locations around the
>Southeast
>>> Region.
>>>
>>> We have installed a SatCOLT positioned in the area of the CO
>NSVLTNMT
>>> building and is up and taking traffic to aid in communication. The
>>> secondary SatCOLT arrived and has been turned up to provide
>additional
>>> coverage.
>>>
>>> The next update will be issued at approximately 13:00 CT, unless
>there is
>>> a significant change in status
>>>
>>> On Fri, Dec 25, 2020, 7:49 PM Ross Tajvar <[email protected]> wrote:
>>>
>>>> Got this internally, sharing here:
>>>>
>>>> Here is the update from AT&T:
>>>> >
>>>> > The front 1/3rd of their building is structuraly damaged.  That
>>>> includes fiber entry.
>>>> > They have no power and there is major flooding on all floors
>including
>>>> the basement.
>>>> > The Fire Department is en route with pump trucks to help with the
>>>> flooding.
>>>> > They have Building Engineers and Electricians on the way to  look
>into
>>>> the structure and getting power turned on.
>>>> > They have 2 850KW generators on the way and 2 1MW generators on
>>>> standby.
>>>> > They have new A/C Chillers on the way (Existing Chiller plant was
>>>> destroyed)
>>>>
>>>> On Fri, Dec 25, 2020 at 3:38 PM Jay R. Ashworth via Outages <
>>>> [email protected]> wrote:
>>>>
>>>>> ----- Original Message -----
>>>>> > From: "Kurt Duncan via Outages" <[email protected]>
>>>>>
>>>>> > Anyone else seeing phone or internet issues due to the AT&T
>building
>>>>> being
>>>>> > damaged by the explosion in Nashville ?
>>>>>
>>>>> Let's please continue to confine replies here to specific
>information
>>>>> about
>>>>> network impacts, and keep the speculation threads to -discuss;
>thanks to
>>>>> whomever already started that thread.  I would name them, but the
>>>>> caffeine
>>>>> hasn't kicked in yet.
>>>>>
>>>>> If you're in that building in Nash, we'll be particularly
>interested in
>>>>> anything you're allowed to tell us in between bailing.
>>>>>
>>>>> Cheers,
>>>>> -- jr '<admin/>' a
>>>>> --
>>>>> Jay R. Ashworth                  Baylink
>>>>> [email protected]
>>>>> Designer                     The Things I Think
>>>>>  RFC 2100
>>>>> Ashworth & Associates       http://www.bcp38.info          2000
>Land
>>>>> Rover DII
>>>>> St Petersburg FL USA      BCP38: Ask For It By Name!           +1
>727
>>>>> 647 1274
>>>>> _______________________________________________
>>>>> Outages mailing list
>>>>> [email protected]
>>>>> https://puck.nether.net/mailman/listinfo/outages
>>>>>
>>>> _______________________________________________
>>> Outages mailing list
>>> [email protected]
>>> https://puck.nether.net/mailman/listinfo/outages
>>>
>>

-- 
Sent from my Android device with K-9 Mail. Please excuse my brevity.
_______________________________________________
Outages mailing list
[email protected]
https://puck.nether.net/mailman/listinfo/outages

Reply via email to