We received the same update from the datacenter ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Power remains off at our data center in Secaucus/EWR1 per the local fire marshall.
We have had an electrical failure with one of our redundant UPS' that started to smoke and then had a small fire in the UPS room. The fire department was dispatched and the fire was extinguished quickly. The fire department subsequently cut power to the entire data center and disabled our generators while they and the utility verify electrical system. We have been working with both the fire department and the utility to expedite this process. We are currently waiting on the fire marshall and local utility to reenergize the site. We are completely dependent upon their inspection and approval. We are hoping to get an update that we can share in the next hour. At the current time, the fire department is controlling access to the building and we will not be able to let customers in. ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ _______________________________________________ Outages mailing list [email protected] https://puck.nether.net/mailman/listinfo/outages