Embarrassing I should have just said open all loading bays and open a huge section of roof should pull in way more than enough cooling at this point. Or don't they have that new kickass roofing ?

-- 
 J. Hellenthal

The fact that there's a highway to Hell but only a stairway to Heaven says a lot about anticipated traffic volume.

On Jan 14, 2024, at 21:44, J. Hellenthal <[email protected]> wrote:

Damn tear the fricken roof off!!!

Not the whole damn thing you psychos just small redirected sections to push in a wanted direction. If needed active your own equipment first ! 
-- 
 J. Hellenthal

The fact that there's a highway to Hell but only a stairway to Heaven says a lot about anticipated traffic volume.

On Jan 14, 2024, at 21:21, Ross Tajvar via Outages <[email protected]> wrote:


They tried that:
IBX Critical Facility Engineers have deployed all available floor fans, opened all available doors and have engaged local rental company to source additional fans and portable spot coolers.

On Sun, Jan 14, 2024 at 10:19 PM Jay Ashworth via Outages <[email protected]> wrote:
Open the doors?


On January 14, 2024 9:52:24 PM EST, Mike Hammett via Outages <[email protected]> wrote:
IBX: CH1
IBX Address: 350 E Cermak Rd, Chicago, 60616
Number: INC0025932
Date and Time of Occurrence: 2024-01-14 08:20:49 Site Local Time

To view the incident and its updates, please use Service Insight. 
New update on Incident INC0025932: Equinix IBX Site Staff reports that temperatures have stabilized with an average temperature of 120 F degrees. One chiller is now fully operational, and another chiller is online but operating at reduced capacity. Equinix IBX Critical Facility Engineers continue to work on restoring the required 4-out-of-6 chillers to return cooling back to normal operations. Portable chillers are currently enroute with an estimated arrival time of 21:00 Site Local Time. Upon arrival, IBX Critical Facility Engineers and our vendor partner will work diligently to get the portable chillers online as quickly as possible. We will send another update once the portable chillers are operational. 

If not already implemented, Equinix site staff highly recommends that customers power down non-essential loads within the data center and/or transfer those operations to backup sites to assist with efforts at lowering the temperature within the facility. 

The severe weather in the Chicago area, contributing to the initial failure, continues to hamper efforts at resolution, but our teams are working diligently to resolve the issue as quickly as possible. IBX Critical Facility Engineers continue to supply outside air to decrease the collocation area's temperature, and all fans have been deployed to support cooling the IBX.
Service Offering: CH1 - Location - Floor
Affected Assets: 05
Asset Condition: Temperature above operating range
Situation status: Under investigation

The next update will be provided in approximately 30 minutes or earlier if available.



From: "Mike Hammett via Outages" <[email protected]>
To: "outages" <[email protected]>
Sent: Sunday, January 14, 2024 2:04:51 PM
Subject: [outages] Equinix CH1 Overheating

Equinix CH1 is overheating due to some chiller failures. The vendor is on-site troubleshooting. Ambient temperature is currently 28 degrees higher than normal.


_______________________________________________
Outages mailing list
[email protected]
https://puck.nether.net/mailman/listinfo/outages

--
Sent from my Android device with K-9 Mail. Please excuse my brevity.
_______________________________________________
Outages mailing list
[email protected]
https://puck.nether.net/mailman/listinfo/outages
_______________________________________________
Outages mailing list
[email protected]
https://puck.nether.net/mailman/listinfo/outages
_______________________________________________
Outages mailing list
[email protected]
https://puck.nether.net/mailman/listinfo/outages

Reply via email to