Yes, I've also run into the G/N bonding inside wiring issue before. The error mssg on the UPS was "wiring fault". In that case moving the UPS to another outlet solved the problem as the wiring issue was only on the outlet.
Tripplite does recommend a specific UPS for use with a generator. It's called an "on-line, double conversion UPS." So that also might be something worth looking into. On Thu, Sep 24, 2020 at 7:08 PM Chuck Hast <[email protected]> wrote: > Ahh forgot the G/N bonding, in the industrial environments I > worked in, we never saw that one it was caught prior to hotting > up the circuit, but indeed home installations are a crap shoot. > > Indeed the home I bought where I now live was like that I had > to make sure the G/N bond was solid as it looked more like an > afterthought. Now it is a bazen thought... > > > On Thu, Sep 24, 2020 at 8:54 PM Michael Barnes <[email protected]> > wrote: > > > You need to verify the wiring from your generator through the transfer > > panel. Depending on how it is configured, it is possible the ground does > > not make it all the way through when on generator. This can easily be > > checked with one of those 3 light circuit testers. I have run into this > in > > the field using generators. In many generators, the ground and neutral > are > > not bonded. A UPS will see this as a fault and not accept the power. > > > > For a building, a transfer panel may be wired a couple of different ways. > > For a large "whole house" system, the transfer panel simply switches > > between commercial power and a big generator prior to the main service > > panel. In that case, the ground-neutral bond takes place in the service > > panel and all should be good. In some cases, however, the generator is > not > > big enough for the whole house. In those situations, there will be a sub > > panel for the "priority" circuits. The transfer switch then toggles > between > > the feed from the main service panel and the generator. Sometimes, the > > transfer panel is wired incorrectly and does not provide the G-N bond > when > > on the generator. > > > > Most modern generators are pretty well regulated, so the UPS rejecting > due > > to frequency or voltage is not likely. (Unless it is a cheapo Harbor > > Freight or similar generator.) > > > > Working a lot of field communications activity and back-up power for > > critical sites, I have run into this quite often. > > > > Check the wiring before worrying about power conditioners. > > > > My $.0002, > > > > Michael > > > > > > On Thu, Sep 24, 2020, 18:16 Mike C. <[email protected]> wrote: > > > > > You shouldn't have to buy anything to fix this problem. You should be > > able > > > to accomplish this by adjusting the governor / idle speed of the > > generator > > > to the rpm that produces a stable 60 hz signal. > > > > > > Ideally, you'd have a cheap multimeter to use to quickly and easily > dial > > in > > > the rpm but if not, you could just try playing around with it until the > > > battery accepts the signal and starts charging. > > > > > > On Thu, Sep 24, 2020 at 5:56 PM Dick Steffens <[email protected]> > > > wrote: > > > > > > > During the fire event last week we were without PGE power a couple of > > > > times. We have a generator connected to the house through a transfer > > > > panel which worked fine for everything except the battery backup > units > > > > we have for our computers. They rejected the power that wasn't a > stable > > > > 60 Hz. I have now heard that this is not uncommon with some > generators, > > > > and that there are devices one can use between the wall outlet and > the > > > > battery backup to maintain clean power. > > > > > > > > Searching for these online is proving to be challenging. Some people > > > > call them inverters. The hits I get for inverters are for converting > > 12v > > > > to 120v. I tried power conditioner. That seems to be what I need, > but I > > > > call upon the collected wisdom of this group for confirmation, or a > > > > suitable clue stick. > > > > > > > > The two search hits I looked at are: > > > > > > > > https://www.newegg.com/p/pl?d=120+volt+line+conditioner > > > > > > > > and > > > > > > > > > > > > > > > > > > https://www.amazon.com/Tripp-Lite-Conditioner-Regulation-LS606M/dp/B00006B83G > > > > > > > > Further thoughts appreciated. > > > > > > > > -- > > > > Regards, > > > > > > > > Dick Steffens > > > > > > > > _______________________________________________ > > > > PLUG: https://pdxlinux.org > > > > PLUG mailing list > > > > [email protected] > > > > http://lists.pdxlinux.org/mailman/listinfo/plug > > > > > > > _______________________________________________ > > > PLUG: https://pdxlinux.org > > > PLUG mailing list > > > [email protected] > > > http://lists.pdxlinux.org/mailman/listinfo/plug > > > > > _______________________________________________ > > PLUG: https://pdxlinux.org > > PLUG mailing list > > [email protected] > > http://lists.pdxlinux.org/mailman/listinfo/plug > > > > > -- > > Chuck Hast -- KP4DJT -- > I can do all things through Christ which strengtheneth me. > Ph 4:13 KJV > Todo lo puedo en Cristo que me fortalece. > Fil 4:13 RVR1960 > _______________________________________________ > PLUG: https://pdxlinux.org > PLUG mailing list > [email protected] > http://lists.pdxlinux.org/mailman/listinfo/plug > _______________________________________________ PLUG: https://pdxlinux.org PLUG mailing list [email protected] http://lists.pdxlinux.org/mailman/listinfo/plug