Palo Verde provides the following response:

>  RCA Tool Control and Decontamination of Tools

1.      What type of decontamination facility is used for tool decontamination? 
  We have an actual Decon Laundry Building designed for decontamination 
purposes.  The building has a spray booth, ultrasonic sink, all liquid wastes 
are collected are pumped to the liquid radwaste system for processing. The 
building has a receiving area for bagged and contaminated equipment and a large 
laydown area for decontamination preparation work.  The building has a 
stainless steel decon spray booth, where large assemblies can be washed down by 
means of steam or high pressure liquids in an enclosed, controlled environment. 
The exhaust is ducted to the filtered exhaust HVAC system.  There is also a 
stainless steel work bench and sink for decontamination of small items, an 
ultrasonic cleaning system consisting of ultrasonic generator and immersible 
transducers and two 4-foot x 4-foot x 3-foot deep stainless steel tanks, a 
liquid abrasive decontamination unit, and a large area for storage of tools and 
decontamination supplies.

Additional, each unit has a Hot Machine Shop with a decontamination spray booth 
similar to the one in the decontamination facility, an ultrasonic cleaning 
system and a 2-foot 6-inch x 12-foot x 3-foot deep stainless steel dip tank; a 
portable pressure washer and a steamerette for equipment decon.

2.      What types of tools are most frequently released from the RCA?  (I&C 
instruments/torque wrenches or gauges, Specialty tools, etc.) As a matter of 
policy, we do not allow common tools to be released from the RCA.  We allow 
specialty tools, e.g., I&C equipment, torque wrenches, M&THE gauges, etc.

3.      What are the fixed and smearable limits for tools and equipment 
maintained in the RCA? 20k fixed, < 1k loose.

 How are tools surveyed for fixed contamination prior to their return to the 
RCA Tool Room - i.e. SAM-9, Cronos-4, frisked, or other method? Tool monitor

 Is there a different fixed contamination limit for Containment vs. Auxiliary 
Building tools? Yes

4.      For Tools used during refueling outages, are they just stored for the 
next outage or are they deconned and put back into use in the RCA?  If stored, 
how are the tools and equipment stored?  Following outage activities tools are 
decontaminated as needed and returned to storage, typically in Sea Vans.  We 
set up a Containment Building access area on ground level outside of the lower 
personnel access hatch.  The Sea Vans are staged, stacked (2 high) and a 
temporary tent enclosure is built around them.  We extend the Containment 
Building CA to include this area.

5.      How are safety harnesses (i.e., fall protection) controlled?  Does the 
plant designate specific harnesses to be used in "contaminated" areas and 
different harnesses for "clean" areas?  What are the contamination limits 
(fixed and loose as applicable) for harnesses used in clean and contaminated 
areas?  Harnesses are segregated for use as either in a contaminated area or 
clean areas within the RCA.  For clean areas, no detectable contamination is 
allowed, for harnesses used in contaminated areas < 20k fixed, no loose.

6.      What process is used for tool decon?  Hand decon, Ultra-sonic sink, 
plas-blast or grit blast unit, or pressure washers?  All of the above.

7.    Are Advanced Radworkers (ARWs) allowed to survey and release tools and 
equipment, or only RP Technicians? Only qualified Sr. RP Technicians

7.      Contaminated Calibrated tools - how are they stored?  Is there a "hot" 
calibration lab in the RCA?  Does the plant conditionally release "fixed" 
contaminated calibrated tools from the RCA to be re-calibrated in the protected 
area?  Each unit has a hot calibration facility.  If the item cannot be 
calibrated in the RCA we conditional release process to allow calibration at 
our central cal facility within the Protected Area.
Seth.
**********************************************************************
Seth J. Kanter, CHP, RRPT
Sr. Health Physicist
Palo Verde Nuclear Generating Station
Mail Sta. 7397
5801 S. Wintersburg Rd.
Tonopah, AZ 85354
Phone (623) 393-3130
Fax (623) 393-1853
Unless otherwise noted, all opinions are my own
Liviu Librescu
**********************************************************************




From: [email protected] [mailto:[email protected]] On Behalf Of 
Barber, Jerry
Sent: Friday, May 27, 2011 5:33 AM
To: [email protected]
Subject: Powernet: Robinson Benchmark - RCA Tool Control and Tool 
Decontamination

Sorry for having to repost, I forgot to include the Subject

Lot of great benchmarks on Powernet right now, here's another.  Good friend of 
mine needs help with his, please help if you can.......thanks!




>  RCA Tool Control and Decontamination of Tools



1.      What type of decontamination facility is used for tool decontamination? 
 i.e. Kelly enclosure type building, stainless steel decon room/trailer, or 
other type decon facility.



2.      What types of tools are most frequently released from the RCA?  (I&C 
instruments/torque wrenches or gauges, Specialty tools, etc.)



3.      What are the fixed and smearable limits for tools and equipment 
maintained in the RCA?

 How are tools surveyed for fixed contamination prior to their return to the 
RCA Tool Room - i.e. SAM-9, Cronos-4, frisked, or other method?



 Is there a different fixed contamination limit for Containment vs. Auxiliary 
Building tools?

4.      For Tools used during refueling outages, are they just stored for the 
next outage or are they deconned and put back into use in the RCA?  If stored, 
how are the tools and equipment stored?



5.      How are safety harnesses (i.e., fall protection) controlled?  Does the 
plant designate specific harnesses to be used in "contaminated" areas and 
different harnesses for "clean" areas?  What are the contamination limits 
(fixed and loose as applicable) for harnesses used in clean and contaminated 
areas?



6.      What process is used for tool decon?  Hand decon, Ultra-sonic sink, 
plas-blast or grit blast unit, or pressure washers?



7.    Are Advanced Radworkers (ARWs) allowed to survey and release tools and 
equipment, or only RP Technicians?



7.      Contaminated Calibrated tools - how are they stored?  Is there a "hot" 
calibration lab in the RCA?  Does the plant conditionally release "fixed" 
contaminated calibrated tools from the RCA to be re-calibrated in the protected 
area?

--- NOTICE ---

This message is for the designated recipient only and may contain confidential, 
privileged or proprietary information.  If you have received it in error, 
please notify the sender immediately and delete the original and any copy or 
printout.  Unintended recipients are prohibited from making any other use of 
this e-mail.  Although we have taken reasonable precautions to ensure no 
viruses are present in this e-mail, we accept no liability for any loss or 
damage arising from the use of this e-mail or attachments, or for any delay or 
errors or omissions in the contents which result from e-mail transmission.

Reply via email to