Here is an approach called the Z-bus approach which is a generalized Thevenin method used for fault analysis of power grids.
Take node 3 as a reference and write a nodal admittance matrix
In this case node 0 ties to nodes 1 and 2 but not to the reference node 3
In the matrix we have at node 0 the sum of the admittances (1/R) to each node connected to it. and the off diagonal admittances are - the branch admittances
row 0 is then 2 _1 _1  (0 is connected to 1 and 2)
row 1 is then _1 2 0 ( node 1 is connected to 0 and reference but not to 2)
row 2 is  _1 0 2  node 2 is connected to 0 and reference but not to 1

so we get
   y=:>2 _1 _1;_1 2 0; _1 0 2
   y
 1 _1  0
_1  3 _1
 0 _1  2

Now invert:
   %.y

  1  0.5  0.5
0.5 0.75 0.25
0.5 0.25 0.75
Since 3 is the reference the resistance from 1 to 3 is the diagonal value

   (<0;0){z
1
The resistance from 1 to 3 and from 2 to 3 is 0.75

This can be extended to large networks and in such cases, the Z bus matrix is built piece by piece avoiding inversion of a large matrix.